[RE-wrenches] Cat 5 cable in 240 AC power conduit with #2 alum entrance wire.
August Goers
august at luminalt.com
Mon Aug 22 11:05:07 EDT 2016
John,
I’m assuming that you’ve got a mix of household voltages (120 or 240 volts)
and low voltage cat-5 cable. You can’t do that, here is the code:
*NEC 300.3(C)(1) Conductors of Different Systems. 1000 Volts, Nominal, or
Less.* Conductors of ac and dc circuits, rated 1000 volts, nominal, or
less, shall be permitted to occupy the same equipment wiring enclosure,
cable, or raceway. All conductors shall have an insulation rating equal to
at least the maximum circuit voltage applied to any conductor within the
enclosure, cable, or raceway.
If you have 600 volt rated shielded cat-5 cable you might be okay.
Separately, it sounds like the grid-tied setup you explain below of
disconnecting batteries from the grid when they are full may not be a good
idea either. Normally you would keep batteries topped off and connected to
the grid for a grid-tied battery backup system. Can you elaborate on what
the customer is trying to accomplish by this control scheme?
Best,
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *John Blittersdorf
*Sent:* Monday, August 22, 2016 6:26 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Cat 5 cable in 240 AC power conduit with #2 alum
entrance wire.
Wrenches,
I have a customer who has pulled a cat 5 cable through his power conduit
(2" PVC) to a new barn for about 120' and wants to use it for ethernet and
telephone. Wants me to use a pair if wires in the cable to trigger a relay
to disconnect a direct grid tie inverter (AC Coupling) when batteries are
full on his double GVFX3648 backup system He wants it in writing from
experts that it is not a good idea. Has anyone done this and had good luck
with it or have opinions?
John Blittersdorf
formerly owner of Central Vermont Solar & Wind
now working for the new owner Rob Stubbins Solar
(I get a regular paycheck and (usually) regular hours.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160822/c2e227ff/attachment.htm>
More information about the RE-Wrenches
mailing list