[RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

jerrysgarage01 jerrysgarage01 at gmail.com
Tue Aug 16 15:10:20 EDT 2016


Wrenches
We have done transformers for issues just like this with good results, the cost vs the new wire, conduit and trenching must be done to make sure which direction. We have had to use paired mcm 300 to make residentual so run the numbers
Jerry


Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone

<div>-------- Original message --------</div><div>From: Chris Schaefer <chris at solarandwindfx.com> </div><div>Date:08/16/2016  7:53 AM  (GMT-10:00) </div><div>To: RE-wrenches <re-wrenches at lists.re-wrenches.org> </div><div>Subject: Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage	drop? </div><div>
</div>Perhaps I missed it but you didn't say what you measured the voltage to be at the clients service entrance panel at his house?

Christopher

On Tue, Aug 16, 2016 at 1:40 PM, Mac Lewis <maclewis1 at gmail.com> wrote:
Yes, what current did you use to calculate that voltage drop? How big is the PV system?


On Aug 16, 2016 11:38 AM, "Chris Mason" <cometenergysystems at gmail.com> wrote:
How much of the power produced will be self-consumed, how much will be exported?

On Tue, Aug 16, 2016 at 12:16 PM, Howard Arey <scot.arey at solarcentex.com> wrote:
Good day,

 

I have a potential client that has an existing 1,000 foot run from the meter and transformer at the street to the home. This is 4/0 Al and quick calcs show the voltage drop at over 12%. He acknowledges that the wire is undersized to keep voltage at/about 240 volts (I have not measured directly at the street / transformer yet).

 

I know the wire has the necessary ampacity to carry his current service needs and to carry amps from the to-be-suggested solar system.

 

My concern is that the voltage drop will change the 240 volts at the street/transformer/meter to 211ish (or will I see a higher 268’sh voltage at the far house end?) at the house. The inverter will try to synch to this voltage but of course this is outside of typical inverter parameters.

 

So, instead of re-running much large wire, does anybody have experience and comments about potentially using a buck-boots transformer at the home to get us back to 240 volts? This would need to be service entrance sized.

 

Howard “Scot” Arey

Owner, Solar CenTex

254-300-1228

scot.arey at solarcentex.com

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com
264.235.5670
869.662.5670
Skype: netconcepts

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





-- 
Chris Schaefer’s

Tel/Fax 585-229-2083 or Cell 585-748-1870 
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com ~ E-mail: chris at solarandwindfx.com



Thomas Jefferson, the author of our great Constitution, once said, "democracy" will cease to exist when you take away from those who are willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160816/f0cf4819/attachment.htm>


More information about the RE-Wrenches mailing list