[RE-wrenches] Enphase Support Non-Responsive

Solar dahlsolar at gmail.com
Sat Aug 6 12:03:39 EDT 2016


I've done a few SE systems lately and I do like it over the micros. Especially with our extremely cold winters. The clipping was getting ridiculous. 
I have a few Tigo systems in as well and like those too. 
Jesse Dahl

NABCEP PV Installation Professional
IBEW Local 292 - Electrician 
Electrical/Solar PV Instructor - HCC

Sent from my iPhone

> On Aug 6, 2016, at 7:14 AM, Howard Arey <scot.arey at solarcentex.com> wrote:
> 
> Aw, one more Enphase  / SolarEdge response.
> 
> The "high voltage" DC is 350-380 volts and with the rapid shutdown capability now shipping standard with SE inverters, they go to 1 volt per optimizer when the AC grid is not present.  By the way, that 1 volt per optimizer is a great way during installation to confirm proper connections - string of 10 means an installer should see 10 volts.
> 
> No bottle neck issue. The optimizer in essence is doing the MPPT function at each module. So if shading, the Opt "finds" best voltage to maximize power output. No string degradation. Mixing modules is not a factor whatsoever.
> 
> Best part is that since I only MPPT on roof and don't invert, I have a string inverter on the side of the house that only does one function - invert! Why try to invert DC to AC on a HOT roof when I could do it with a much higher efficiency box that is more robust on the side of the house or in a garage?
> 
> I've gone away from microinverters entirely - too many nuisance faults. And each nuisance fault is a phone call to customer support that is handling more than they can handle by a ratio of...number of MLPE to string inverters essentially. 
> 
> Scot
> Solar CenTex
> 
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Dorsett
> Sent: Friday, August 5, 2016 1:46 PM
> To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Enphase Support Non-Responsive
> 
> Still you pay as much for the Solar Edge optimizers as for Enphase inverters plus you have the cost of the central inverter.  At some point you are still dealing with high voltage DC, so safety is far better with off the roof 240V AC; you still have the bottleneck if one module is shaded or corroded; and you still have the difficulty of replacing a legacy module to build a compatible string. Again I am not unhappy about Enphase hardware. I just think they've grown too fast to keep their support as well organized as the rest of the company.
> 
> Bill Dorsett
> Manhattan, KS
> 
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of penobscotsolar at midmaine.com
> Sent: Friday, August 05, 2016 12:54 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Enphase Support Non-Responsive
> 
> It is a very simple install. With SolarEdge there is no trunk cable, which definitely cuts down on wire management, especially using SnapNRack mounting. Everything is MC4, so PV wire to a transition box, to the inverter input(s) make it pretty simple. We almost always mount our inverters outside, even when they are string inverters, and typically on the north side of the home/business. My guys didn't like the changeover on the first SolarEdge job, but it only took one to bring them around and they are now converts.
> 
> Daryl
> 
> 
>> Do you find that the installation takes longer because you're 
>> basically installing a micro inverter and string inverter system at the same time?
>> I've also heard of AHJ's requiring that the inverter be mounted 
>> outside because of the rapid shutdown disconnect attached to the inverter.
>> 
>> Thanks,
>> Will
>> 
>> 
>> --
>> *Will White*
>> Curriculum Developer
>> 
>> e: will at solarenergy.org
>> w: www.solarenergy.org
>> p: 802-272-3092
>> 
>> PV Installation Professional
>> # 093006-34
>> 
>>> On Fri, Aug 5, 2016 at 1:41 PM, <penobscotsolar at midmaine.com> wrote:
>>> 
>>> Since I am having such a tough time even getting a call back, never 
>>> mind reimbursments, we have started very happily using SolarEdge with 
>>> very good results so far. Communications, no problem, occasional tech 
>>> support is timely, we are seeing less than a 1% failure on 
>>> optimizers. Ease and safety of installation is excellent as 
>>> well....and no, I don't work for them :-)
>>> 
>>> Daryl
>>> 
>>> 
>>> 
>>>> Wrenches
>>>> We have allot of enphase and ya sometimes it a little hard to get 
>>>> them
>>> on
>>>> the line but we always do. I request the re-inbursments, l dont 
>>>> ever
>>> see
>>>> them as they end up in the admin office. We have looked at and used 
>>>> a
>>> few
>>>> other mico-inverters at customer request but they all seem to go 
>>>> out
>>> of
>>>> business so we are sticking to enphase for better or worse.
>>>> Jerry
>>>> 
>>>> 
>>>> Sent via the Samsung Galaxy Sâ„¢ III, an AT&T 4G LTE smartphone
>>>> 
>>>> <div>-------- Original message --------</div><div>From: Wayne Irwin 
>>>> <wayne at pureenergysolar.com> </div><div>Date:08/05/2016  6:58 AM
>>>> (GMT-10:00) </div><div>To: re-wrenches at lists.re-wrenches.org
>>>> </div><div>Subject: Re: [RE-wrenches] Enphase Support 
>>>> Non-Responsive </div><div> </div>Maybe just dumb luck, but we 
>>>> almost always have quick phone tech support from Enphase and always 
>>>> get reimbursed.
>>>> 
>>>> Wayne Irwin
>>>> Pure Energy Solar
>>>> 
>>>> Sent from my mobile device
>>>> 
>>>> From: conradg at cape.com
>>>> Date: Fri, 5 Aug 2016 12:39:02 -0400
>>>> To: re-wrenches at lists.re-wrenches.org
>>>> Subject: Re: [RE-wrenches] Enphase Support Non-Responsive
>>>> 
>>>> Same thing going on here
>>>> 
>>>> Conrad
>>>> Cotuit Solar
>>>> 
>>>> 
>>>> Conrad Geyser, Principal
>>>> Cotuit Solar LLC
>>>> 508-428-8442
>>>> 
>>>>> On Fri, Aug 5, 2016 at 9:59 AM, gary easton <gary at arp-solar.com>
>>>> wrote:
>>>> just a worthless ticket but no action and certainly no timely
>>>> reimbursement if at all.   I would never do business with this company
>>>> again.
>>>> 
>>>> On Fri, Aug 5, 2016 at 9:38 AM, <penobscotsolar at midmaine.com> wrote:
>>>> Just to renew this line of conversation, I have been waiting for
>>> several
>>>> call backs form Enphase, with no results, for the past three weeks. 
>>>> I
>>> also
>>>> have warranty claims that go back four months+ that have not been 
>>>> fulfilled. I will not sell any more Enphase, at all, until they
>>> resolve
>>>> these communication and warranty issues.
>>>> 
>>>> Daryl DeJoy
>>>> NABCEP Certified PV Installer
>>>> Penobscot Solar Design
>>>> 
>>>> 
>>>> 
>>>> 
>>>>> It seems like we are talking about inverter and module customer
>>> service
>>>>> (good and bad) a lot lately.
>>>>> 
>>>>> Has anyone else noticed that Enphase seems to have stopped 
>>>>> responding
>>> to
>>>>> tickets submitted via their website? Hold times are unacceptable, 
>>>>> so
>>> I
>>>>> gave
>>>>> up on that, but nobody gets back to you when you try to contact 
>>>>> them
>>> via
>>>>> their web form for weeks, even about an existing RMA or ticket, 
>>>>> and
>>> they
>>>>> no
>>>>> longer let you update tickets by email. They are very helpful and 
>>>>> competent if you get them on the phone, but who has time for 
>>>>> that?!
>>>>> 
>>>>> I'm also waiting an unacceptable amount of time on a major module 
>>>>> manufacturer warranty claim right now. I'd love to see Home Power 
>>>>> or someone do a story on manufacturer responsiveness to dealers.
>>>>> Things
>>> are
>>>>> generally going down hill it seems.
>>>>> 
>>>>> Jason Szumlanski
>>>>> Florida Solar Design Group
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.o
>>>>> rg
>>>>> 
>>>>> List-Archive:
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>>> org/maillist.html
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
>>>> g
>>>> 
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>>> org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>>> 
>>>> 
>>>> 
>>>> --
>>>> Gary Easton
>>>> Appalachian Renewable Power
>>>> Stewart, Ohio 45778
>>>> NABCEP Certified Solar PV
>>>> T: 740-277-8498
>>>> www.arp-solar.com
>>>> 
>>>> “First they ignore you. Then they laugh at you. Then they 
>>>> fight
>>> you.
>>>> Then you win.â€
>>>> 
>>>> ~Ghandi
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
>>>> g
>>>> 
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>>> org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>>> 
>>>> 
>>>> 
>>>> _______________________________________________ List sponsored by
>>> Redwood
>>>> Alliance List Address: RE-wrenches at lists.re-wrenches.org Change
>>> listserver
>>>> email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
>>>> g
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>>> org/maillist.html
>>>> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check 
>>>> out
>>> or
>>>> update participant bios:
>>>> www.members.re-wrenches.org_________________________________
>>> ______________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
>>>> g
>>>> 
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>>> org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>>> org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>> 
>> 
>> --
>> *Will White*
>> Curriculum Developer
>> 
>> e: will at solarenergy.org
>> w: www.solarenergy.org
>> p: 802-272-3092
>> 
>> PV Installation Professional
>> # 093006-34
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>> .html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 


More information about the RE-Wrenches mailing list