[RE-wrenches] Replacing grounded inverters
jay
jay.peltz at gmail.com
Sun Jul 24 11:41:25 EDT 2016
I’m curious about it happening at the same time each day. I think that is a big clue.
Could it be some other interference from some other electrical part? Motors etc?
And what about if its heat related? IE the roof/modules heating up causing the issue?
Curious.
jay
peltz power
> On Jul 24, 2016, at 8:37 AM, Drake <drake.chamberlin at redwoodalliance.org> wrote:
>
> It could easily be a nuisance trip rather than any problem. For sure, you want to check for possible problems. Big metal roofs are prone to nuisance tripping of the SMA AFCIs. I've been through this.
>
> At 09:35 PM 7/23/2016, you wrote:
>> Content-Type: multipart/alternative;
>> boundary="----=_NextPart_000_0001_01D1E52A.1853FE80"
>> Content-Language: en-us
>>
>> Hi Jerry,
>>
>> It passes the initial power up tests fine, and fails at almost the same time of day when it faults with a 4301 Electric Arc Detected. Not usually the next day, often it will be fine for a week or so.
>> According to the web box, the inverter has the latest available firmware.
>> I am hoping it is a failure at a splice in a rooftop jbox (all are exposed on the ridge).
>> I went there last week, but the customer office manager decided she wanted a written safety plan before she was comfortable letting me climb on the roof, so I am cogitating on that.
>>
>> Thanks for your thoughts.
>> Glenn
>>
>> From: Jerry Shafer [ mailto:jerrysgarage01 at gmail.com <mailto:jerrysgarage01 at gmail.com>]
>> Sent: Friday, July 22, 2016 11:05 PM
>> To: RE-wrenches; glenn.burt at glbcc.com
>> Subject: Re: [RE-wrenches] Replacing grounded inverters
>>
>>
>> Question, is it the first test where it is checking for noise in the system or is it finding a fault once it is running. Does it have the latest software update, which code do you have test failure or arc failt detected, way different trouble shooting tracks yo follow. If it is a test fail try to remove just the ground wire from the array, because its a metal roof its a big antenna and hears something that is to much for the test to deal with. If it fails due to an arc then there is most likely an arc at a connection.
>>
>> Jerry
>>
>> On Jul 22, 2016 3:37 PM, "Glenn Burt" <glenn.burt at glbcc.com <mailto:glenn.burt at glbcc.com>> wrote:
>> August,
>>
>> I am currently chasing down unexplained AFCI faults with old SX 160 modules on a metal roof and having replaced two SMA SWR-2500Uâs with a SB 5000TL-US-22. So far I have been swapping input strings to see if there is a pattern, however no joy.
>> Next visit is up on the roof (steep pitch) to see if there is anything obvious.
>> I hate to simply disable the AFCI functionality without a serious effort, however I am approaching that point.
>> It is a T&M job for a system installed by others back in 2004, about an hour trip 1 way and I am afraid the customer will soon believe I am stringing out the work.
>>
>> Looking forward to hearing more of your experience as it develops!
>>
>> -Glenn
>>
>> From: RE-wrenches [ mailto:re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of August Goers
>> Sent: Friday, July 22, 2016 10:23 AM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] Replacing grounded inverters
>>
>> Glen,
>>
>> Itâs interesting you mention that youâre having AFCI issues with new TL inverters and old modules. We are too. We have a particular system with BP modules where weâre trying to figure out if we have a warranty claim situation. Weâve cleaned up all the DC-side wiring and still the Sunny Boy is tripping with AFCI errors. We think it is either corroded traces in the modules or perhaps bypass diode issues in the module j-boxes. More to come.
>>
>> August
>>
>> From: RE-wrenches [ mailto:re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of Glenn Burt
>> Sent: Friday, July 22, 2016 5:08 AM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] Replacing grounded inverters
>>
>> If you read some of the proposed changes for the 2017 NEC, it is looking life there will be no problem replacing isolated inverters with non-isolated versions. In fact the proposed wording seems to allow either USE, or PV wire to be used with non-isolated inverters explicitly going forward.
>> It made me feel better about doing recent replacements.
>> I'm having more trouble with the TL inverters and AFCI issues on older systems, however.
>> From: Gary at Santa Ynez Valley Solar <mailto:Gary at SYVSolar.com>
>> Sent: â7/â21/â2016 21:43
>> To: re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>
>> Subject: [RE-wrenches] Replacing grounded inverters
>> We are all facing having to replace the old transformer based inverters when they run out. Really difficult to find replacements. Against code to replace with transformer less ones. I wonder if a DC/DC transformer could be installed just ahead of the transformer less inverter for isolation purposes? Not clear on the concept.
>>
>>
>> Gary
>>
>>
>> Gary Gordon
>>
>>
>> www.SYVSolar.com <http://www.syvsolar.com/>
>> PO Box 688
>> Santa Ynez, CA 93460
>> 805 688-1213 <tel:805%20688-1213>
>> NABCEP Certified Installer
>> CA Licensed Solar Contractor
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>_______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160724/4ce6f2a9/attachment.htm>
More information about the RE-Wrenches
mailing list