[RE-wrenches] array overloading of an inverter
Daniel Young
dyoung at dovetailsolar.com
Wed Jul 13 16:37:35 EDT 2016
I'm with Matt in terms of Design. I use 1.2-1.35 as a general rule. With
current inverter sizes, you almost always can get a good fit within this
range.
Climate plays a big role on this. As do the costs of your materials and
labor. What we use as guidance is this:
[If I save 5% on a systems cost by going with a smaller inverter, and the
"clipping" losses are only 2% of my yearly energy, then the tradeoff is
worth it. I produce more kWh for the dollars spent.]
The above is a simplistic view not using real numbers (don't have time right
now to run costs on different options in you climate :) ) You can also think
about how the inverter life is affected by operating closer to its limits
for a longer amount of time each year, but that is a hard variable to
quantify.
I ran a set of simulations just for kicks on what I believe to be one of
your Jobs Kirk. @ cypress semiconductor. Hopefully to get a better idea of
what these DC:AC ratios mean in your climate.
I put 6.16kW DC of Solar modules on the roof @15degrees (22 x 280W modules).
I ran the simulation with a SB4000TLUS-22, a SB5000TLUS-22, and
SB6000TLUS-22. And I got 3.8%, 0.3%, and 0.0% clipping losses respectively.
Based on the above, my gut says that the 5kW is certainly worth it. And even
the 4k inverter might, but I'm not comfortable going to a 1.5:1 DC:AC ratio
for so many other reasons.....
With Regards,
Daniel Young,
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Matt Partymiller
Sent: Wednesday, July 13, 2016 4:16 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] array overloading of an inverter
Kirk,
I would recommend you consider using a tool like PVsyst or Helioscope to
model DC:AC ratios. A quick modeling of roughly 200 kW on three Solectria
50 kW inverters shows about 1.3% clipping here.
It then comes down to analysis of your costs for additional modules, dc
wiring, and inverters.
Admittedly I sit on the opposite side of the fence. I try to provide at
least a 1.2 ratio to minimize cost per kWh. I am not aware of any large
scale studies comparing PVsyst or Helioscope clipping projections to real
world performance. I can tell you that our arrays with monitoring and a
~1.2 DC:AC ratio perform as well as our older 1:1 systems. Not that I use
Enphase often but they have some research/whitepapers on the topic since
their micros tend to undershoot 60 cell module power ratings.
Good luck!
Matt
Matthew Partymiller
Solar Energy Solutions LLC
(877) 312-7456
matt at solar-energy-solutions.com
On Wed, July 13, 2016 3:02 pm, Kirk Herander wrote:
> Hello folks,
>
>
> I am composing a response to a question a potential customer asked me.
> It seems a competitor is trying to talk him into a 20% larger KW
> array than the inverter AC max output rating is. The idea of course is
> to generate more power on either side of peak output, but at a cost I
> don't feel is justified. My opinion of this particular big-box
> installer I will keep to myself. My response to the customer, trying to
keep it simple:
>
>
>
> "On the DC array input side, most inverters do allow an overload factor.
> For
> instance, a 10kw AC inverter may allow for 12 kw of DC array as an input.
> Whether or not this is a good idea boils down to economics and
> technical reasons.
>
> On a sunny day, the inverter generates power as a typical bell curve.
> Power
> output rises in the morning, peaks at noon, declines in the afternoon.
> In my example, the inverter can't output more than 10 kw AC. What
> overloading the input will do will widen the bell curve, i.e.
> generating more power in the morning and afternoon, BUT clipping the
> peak at 10kw on either side of noon. So there is power to be gained in
> morning and afternoon, but peak power is lost(if conditions allow the
> peak output to be reached), since the 12 kw array can never be converted
to more than 10 kw of AC power.
> Depending upon
> time of year(ambient / cell temperature) and weather conditions, the
> peak may be clipped at 10 kw for several hours a day. So you are both
> gaining and losing power using this method. And typically the
> inverters are only overloaded in this manner on large-scale farms
> where the economics are favorable.
>
> In your case, if you could actually put 200kw of DC array into 150 Kw
> of inverter, the economics would never justify it. That extra 50 kw of
> array would cost you $100k of more, and the dollar payback for the
> power that extra 50Kw would generate will take 2 - 3x the time that
> the array size does that stays inside the output limit of the
> inverters. This is why I'm not a big fan of dramatically overloading
> the inverters, if at all, in your case. Any KW portion of the array
> which is above the nameplate kw rating of the inverter is going to
> have a longer payback for these reasons. "
>
> I feel my reasoning is sound, But I don't want to be too loose with
> the facts. Comments are appreciated. Thanks.
>
>
>
> Kirk Herander
>
>
> Owner|Principal, VT Solar, LLC
>
>
> Celebrating our 25th Anniversary 1991-2016
>
>
> www.vermontsolarnow.com
>
> dba Vermont Solar Engineering
>
> NABCEPTM 2003 Inaugural Certificant
>
>
> VT RE Incentive Program Partner
>
>
> 802.863.1202
>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
> .ht
> ml
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list