On Sat, Jun 18, 2016 at 2:13 PM, Gary Willett <Gary at icarussolarservices.com>
wrote:

>
> Were all of the components in the cabinet factory mounted and
> inter-connected, or was it field assembled?
>
It came assembled. The only hard part was the external production metering.
I would show you a photo except I am not very proud of it.
You have to install the batteries and auxiliary cabinet in place.

> How much does the finished product weigh?
>
About 500lbs before the batteries, we used our crane to lower it down the
stairwell. Two people, a handcart, should be all you need.
https://www.dropbox.com/s/y3wajbo1614f52v/2016-06-09%2014.46.39.jpg?dl=0
https://www.dropbox.com/s/ceodgghk1zcpih2/2016-06-09%2014.47.01.jpg?dl=0
You put the batteries in after you get it in place.


> Do you have any Sonnen and/or Outback URL(s) that provide installation
> documentation and a high level single line electrical block diagram of
> what's inside the box?
>
The owner's manual has all that.
https://www.dropbox.com/s/hhntxsq9kpbr9ot/Ohio%20II%20Installation%20and%20Operation%20Manual%20V1.1.pdf?dl=0


> Thanks! Gary
> On 6/18/16 6:48 AM, Chris Mason wrote:
>
> Here's the internals of the one we installed.
> https://www.dropbox.com/s/m0ie2tuqe7y1x9d/2016-06-15%2011.01.43.jpg?dl=0
> It's a Radian, the batteries are Sony, there's a PLC in the door
> controlling everything, and a Vera Z-Wave controller for the programmable
> outlets.
> The BMS is on the door, connected by the long cable you see at the bottom.
> It's not really long enough, which I complained about.
> The transfer switch is a Generac component, very reliable unit, rated at
> 200A.
> There is a DIN rail next to the inverter that holds all the internal
> wiring, metering, external connections.
> One thing I would advocate, never try to make any connections with this
> unit powered up. It is very tight in there and the risk of touching a live
> terminal is high.
> There is a 200A main breaker and a battery breaker, which is software
> controlled for powering down from the front panel. Startup requires holding
> in a DC breaker for the electronics for a few seconds then engaging the
> main battery breaker. The instructions says five seconds but I find it
> takes about 15.
>
>
>
>
> On Fri, Jun 17, 2016 at 9:54 PM, Gary Willett <
> Gary at icarussolarservices.com> wrote:
>
>> Enclosed is a photo of what appears to be a test/lab Sonnen system
>> published in the 01/30/2016 edition of "Power Magazine.
>>
>> Can plainly see the 8kW Outback Radian inverter and I assume four 12V
>> Sonnen (Sony?) 8kWh Lithium-Ion batteries. Assume this is a "standard" 48V
>> Radian inverter.
>>
>>
>> http://www.powermag.com/german-battery-firm-sonnen-moves-into-u-s-home-solar-storage-market/
>>
>> Regards,
>>
>> Gary Willett
>>
>> Icarus Engineering LLC
>>
>>
>> On 6/17/16 2:09 PM, Chris Mason wrote:
>>
>> Yes, correct on both. The generator support is there, I did not use it.
>>
>> On Fri, Jun 17, 2016 at 3:07 PM, Carl Adams < <swingjunkie at gmail.com>
>> swingjunkie at gmail.com> wrote:
>>
>>> Chris,
>>>
>>> Nice finish on the Sonnen install.  It looks fabulous.  My understanding
>>> is the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW
>>> radian.  I assume generator support is fully supported
>>>
>>> On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason <
>>> cometenergysystems at gmail.com> wrote:
>>>
>>>> I promised a picture of the Sonnen installation. As these units are
>>>> getting close to being appliances in the same vein as home audio, we wanted
>>>> to have a clean finish so we made some mill work to complete the top of the
>>>> unit to the ceiling and hide the ugly conduits.
>>>>
>>>> https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0
>>>>
>>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installerâ„¢
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installerâ„¢
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts