[RE-wrenches] Odd Inverter Problem
Dan Fink
danbob88 at gmail.com
Sat Jun 11 18:46:19 EDT 2016
Since you don't name the inverter OEM, I'm just guessing, but.....the
ground to neutral bond thing can indeed fry what I call "truck top" AKA
"portable" inverters. The puzzling thing in my experience is it can take 6
months......1 month.....1 week......1 second for the failure. Or it might
work fine (but not be to code).
My rule....to connect to a standard AC load panel (no matter how small) the
inverter has to have actual hard-wired AC Out terminals...hot, neutral and
ground. If the only way to connect it to the house AC system is a 120V AC
extension cord with the female end chopped off and hard wired to the load
panel, you are asking for trouble and have left NEC far behind. I got
well-zapped by one these in the past....
Dan Fink
Adjunct Professor of Solar Energy Technology, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Registered Continuing Education Providers™
970.672.4342
On Sat, Jun 11, 2016 at 12:58 PM, Travis Jordan <travis at jordansolar.net>
wrote:
> Just a thought, but some of the old or cheap inverters don't take nicely
> to bonding the ground to neutral. You may try leaving the ground wire
> disconnected from the inverter for a test and see if that changes
> anything.... Also make sure you don't have moisture or a short of some sort
> in your output cable to the house, I got involved with a job once that had
> normal Romex buried outside and it got wet and caused issues with the
> inverter not working properly. It ohmed out fine, but when I hooked it up
> it didn't play nice with the inverter. I would suspect something with the
> site wiring from what I am understanding from your post.
>
> Good luck!
>
> Travis Jordan
> travis at jordansolar.net
> travis at mtsolar.us
>
>
> --
> *Travis Jordan*
> travis at jordansolar.net
> *877-215-8431, Ext. 104*
> *Cell: 406-274-1230*
> *Jordan Solar*
> *jordansolar.net* <http://www.jordansolar.net/>
> [image: Jordan Solar Logo] <http://www.jordansolar.net/>
> Solar PV Installer # 031409-69 <http://www.nabcep.org/>
> MT EL License # ELE-EJ-LIC-9886
> WA EL License# TRAVIJE901PK
> ID EL Masters # 010810
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160611/e27eb9b7/attachment.htm>
More information about the RE-Wrenches
mailing list