[RE-wrenches] Fried Classic150?
Aaron Mandelkorn
reosolar at gmail.com
Tue May 31 16:39:11 EDT 2016
Thanks Bob. We are using agm batteries and everything should have been
turned off including the battery box breakers before the customer left. We
could deal with a few months of self discharge. The array was snow covered
at max tilt due to it being on a hillside and not tall enough. Controller
cycling and inverter brought the system down. This customer also refused to
have his generator hooked up to a auto start module for fear it would be
completely snow covered. Go figure. Pulling the batteries to see if they
are salvageable. Never working with diy homeowners again.
Aaron Mandelkorn
Owner/Solar Specialist
Renewable Energy Outfitters
www.reosolar.com
www.offgriddepot.biz
970-596-3744
719-221-5249
reosolar at gmail.com
On May 31, 2016 2:12 PM, "bob at midnitesolar.com" <bob at midnitesolar.com>
wrote:
Aaron, lead acid batteries will "self discharge". Letting them sit for
more than
a couple of weeks may not be that good for them as they can sulfate without
a good absorb
charge cycle every once in a while at least for a couple of hours.
The inverter and charge controller will always draw some power from the
batteries just being
connected. This is due mainly to the internal auxiliary supplies and
microprocessors. If the main battery
breakers were turned off when the customer left for the winter, the
batteries will still discharge
themselves and start to sulfate but the voltage dropping would not happen
quite as fast.
You might want to add a small backup generator and tilt the PV array more
vertical to help
shed the snow during the winter months if nobody is around to take care of
the system.
boB
On 5/31/2016 10:43 AM, Aaron Mandelkorn wrote:
Thank you everyone for your input. I am quite sure this controller was just
doing what it was supposed to do. The inverter disconnected from low
voltage and the solar modules were covered with snow for months. The
classic was trying to reconnect all this time and I believe acted as a load
on the batteries. Essentially the classic brought the system down but poor
design and actions by the customer are what led to this disaster. I will be
pulling the batteries and changing/ load testing at the shop. Hopefully we
didn't destroy this battery bank.
Aaron Mandelkorn
Owner/Solar Specialist
Renewable Energy Outfitters
www.reosolar.com
www.offgriddepot.biz
970-596-3744
719-221-5249
reosolar at gmail.com
Hi Aaron,
A customer of mine had a very similar situation happen couple years ago,
except with the added fun of frozen batteries, split open and a resulting
mess. (system was installed by others without a proper battery box / spill
containment).
This fault was traced back to a failed MX60 controller that was not only
preventing solar input, but had a small parasitic load on the system that
was enough to discharge the batteries. Replaced controller, new batteries
(with spill containment!) and the system has been fine since.
Kevin
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Aaron Mandelkorn
*Sent:* May-30-16 9:35 PM
*To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
*Subject:* Re: [RE-wrenches] Fried Classic150?
The more I think about this the stranger it seems. All system breakers were
left on before leaving for the winter. Inverter was also on to power two
small AC fans. How can a 48 volt battery bank get so discharged to the
point of almost complete depletion (13.7 volts). The inverter low battery
cutout was programmed to 48.1v and there are no DC loads. Isn't the point
of lbco to protect against this exact situation? What could have brought
this bank down so low? I am wondering if my client may have reset the lbco
and other settings by throwing the inverter breaker by accident.
Aaron Mandelkorn
Owner/Solar Specialist
Renewable Energy Outfitters
www.reosolar.com
www.offgriddepot.biz
970-596-3744
719-221-5249
reosolar at gmail.com
On May 30, 2016 8:43 PM, "Dan Fink" <danbob88 at gmail.com> wrote:
MPPT does need a minimum battery voltage to wake up and start charging, at
least 9 volts -- I once arrived at a remote site on a sunny day, the PV
input breaker had tripped, batteries were under 9v, no charging despite the
sunny weather until I woke the MPPT up with jumper cables from my truck
battery.
Dan Fink
Adjunct Professor of Solar Energy Technology, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Registered Continuing Education Providers™
970.672.4342
On Mon, May 30, 2016 at 5:59 PM, Aaron Mandelkorn <reosolar at gmail.com>
wrote:
Hi all. I returned to a off grid site today after having no winter access.
It appears as though the classic 150 charge controller has failed. The
batteries are completely discharged. The classics screen will flash
occasionally as well as a yellow light on this left front of the controller
but wont turn on. Does the classic have a minimum voltage requirement
needed to turn on? Has anyone else experienced this? I can't figure out
what happened to cause this issue.
Thanks
Aaron Mandelkorn
Owner/Solar Specialist
Renewable Energy Outfitters
www.reosolar.com
www.offgriddepot.biz
970-596-3744
719-221-5249
reosolar at gmail.com
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address &
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:www.re-wrenches.org/etiquette.htm
Check out or update participant bios:www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160531/815356ed/attachment.htm>
More information about the RE-Wrenches
mailing list