[RE-wrenches] Fried Classic150?
bob at midnitesolar.com
bob at midnitesolar.com
Mon May 30 22:53:49 EDT 2016
Yes, the 9V is because of the auxiliary power supply that powers
everything inside. Not just the Classic of course. Lots of voltages and
various
power levels required to run these things.
And charcoal inside a Classic refurb ! Hmmm... You can be sure...
There WILL be spankings !
boB
On 5/30/2016 7:43 PM, Dan Fink wrote:
> MPPT does need a minimum battery voltage to wake up and start
> charging, at least 9 volts -- I once arrived at a remote site on a
> sunny day, the PV input breaker had tripped, batteries were under 9v,
> no charging despite the sunny weather until I woke the MPPT up with
> jumper cables from my truck battery.
>
> Dan Fink
> Adjunct Professor of Solar Energy Technology, Ecotech Institute
> IREC Certified Instructorâ„¢ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Registered Continuing Education Providersâ„¢
> 970.672.4342 <tel:970.672.4342>
>
>
> On Mon, May 30, 2016 at 5:59 PM, Aaron Mandelkorn <reosolar at gmail.com
> <mailto:reosolar at gmail.com>> wrote:
>
> Hi all. I returned to a off grid site today after having no winter
> access. It appears as though the classic 150 charge controller has
> failed. The batteries are completely discharged. The classics
> screen will flash occasionally as well as a yellow light on this
> left front of the controller but wont turn on. Does the classic
> have a minimum voltage requirement needed to turn on? Has anyone
> else experienced this? I can't figure out what happened to cause
> this issue.
>
> Thanks
>
> Aaron Mandelkorn
> Owner/Solar Specialist
> Renewable Energy Outfitters
> www.reosolar.com <http://www.reosolar.com>
> www.offgriddepot.biz <http://www.offgriddepot.biz>
> 970-596-3744 <tel:970-596-3744>
> 719-221-5249 <tel:719-221-5249>
> reosolar at gmail.com <mailto:reosolar at gmail.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160530/0679cbc0/attachment.htm>
More information about the RE-Wrenches
mailing list