The (newer) SW5548 was harder on over current protection, mainly because
it could put out more current than the SW4048...
One trick to try is to place a long(ish) extension cord between the SW
and the load to give it a wee bit of series resistance.
Doing this would often reduce that OCP and help motors to start.
boB
On 5/30/2016 11:03 AM, Dan Fink wrote:
> Does your air compressor have an unloader valve, or can you install one?
> That should do the trick, sounds like you are just running into the
> regular high surge current demand.
> Off the grid, compressors are in about the same nasty league as old
> well pumps as far as surge demand.
>
>
>
>
> Dan Fink
> Adjunct Professor of Solar Energy Technology, Ecotech Institute
> IREC Certified Instructorâ„¢ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Registered Continuing Education Providersâ„¢
> 970.672.4342 <tel:970.672.4342>
>
>
> On Mon, May 30, 2016 at 10:46 AM, Jeremy Rodriguez
> <allsolarjeremy at msn.com <mailto:allsolarjeremy at msn.com>> wrote:
>
> Hello
> I've got an SW+5548 that will barley start my air compressor. Once
> it does run it shows 17 Amps on the inverters loads meter. During
> start up it reads 60+ amps.
> Do you think better capacitors would help the situation?
> BTW I've never ran the compressor off grid prior.
> I even tried #8 from the Breaker to the pressure switch, about
> 9ft, with no benefit. The compressor will only start with the tank
> completely empty.
>
> Jeremy Rodriguez
> Solar Installation And Design Expert
> All Solar, Inc.
> 1463 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand!
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160530/776ba441/attachment.htm>
More information about the RE-Wrenches
mailing list