[RE-wrenches] supply side connection - Tap connector recommendations
Drake
drake.chamberlin at redwoodalliance.org
Thu May 12 09:48:17 EDT 2016
They are also prohibited by AEP Ohio.
At 11:44 AM 5/11/2016, you wrote:
>Hi Kirpal,
>
>Sounds like you are well informed but I thought
>I'd throw this in just in case. In Xcel Energy
>territory in Colorado they specifically prohibit
>piercing taps for solar installations. I'm not
>sure why, but you may want to run it by the
>utility in case there happens to be some solar specific regulation.
>
>Good Luck
>
>On Wed, May 11, 2016 at 9:36 AM, Kirpal Khalsa
><<mailto:solarworks at gmail.com>solarworks at gmail.com> wrote:
>Hi Shasta....Thank you for the
>reminder. Safety first as they say!! Jason hit
>the nail on the head....Coordinating with the
>local utility and inspector is what caused us to
>go the route of the insulation piercing taps in
>the first place....We also considered the
>ConnectDer meter collar.....I am sure we will
>use it in the future....The local utility has
>not already approved their use and in the middle
>of a project we didn't want to break new ground.Â
>Luckily for us our experienced electrician will
>be making the hot taps, I will use the
>opportunity to remind them about safety....
>Cheers!
>
>Sunny Regards,
>Kirpal Khalsa
>Oregon LRT#25
>NABCEP Certified PV Installation Professional
>Oregon Solarworks LLC
><http://www.oregonsolarworks.com>www.oregonsolarworks.com
><tel:541-299-0402>541-299-0402
>
>On Wed, May 11, 2016 at 7:12 AM, Shasta Daiku
><<mailto:mjmorningstar at gmail.com>mjmorningstar at gmail.com> wrote:
>Yes, âI getâ that there is inconvenience in
>coordinating  with the utility and inspectors,
>permitting, and power disruption. In my world
>thatâs just a given part of the process. Of
>course there are circumstances where
>disconnecting a utility supply is nearly
>unavoidable, for instance, certain industrial
>processes that run 24/7. I am aware that the
>practice of installing line side taps on
>energized unfused conductors is common in the
>solar industry and always thought it pretty
>cavalier. I have to wonder just how many
>âinstallersâ have had real training for live
>work and utilize proper personnel safety
>protection. Part of the classwork for this type
>of training is watching/viewing the results of
>things gone wrong, even when the best practices
>are applied. An indelible impression
>will certainly be imprinted, and an attitude of
>"avoiding the avoidableâ second nature.
>
>MichaelÂ
>
>>On May 11, 2016, at 5:24 AM, Jason Szumlanski
>><<mailto:jason at floridasolardesigngroup.com>jason at floridasolardesigngroup.com>
>>wrote:
>>
>>In some jurisdictions and for some utilities,
>>pulling the meter is a MAJOR ordeal. Some
>>jurisdictions require a "service change" permit
>>on top of the solar permit just to have the
>>meter pulled. It also requires getting an
>>inspector out there at the perfect time to have
>>it inspected so the the utility will re-install
>>the meter. The homeowner is often without power
>>for several hours, which is usually somewhere
>>between inconvenient and unacceptable.
>>Insulation piercing taps are extremely common
>>around here for these reasons. With proper
>>safety precautions and experience, I don't see
>>any issue specifying and using them.
>>
>>
>>Jason Szumlanski
>>
>>
>>
>>
>>On Wed, May 11, 2016 at 12:26 AM, Shasta DaikuÂ
>><<mailto:mjmorningstar at gmail.com>mjmorningstar at gmail.com>Â wrote:
>>Kirpal, Iâm curious what the reason is for
>>making the tap on an energized line. Why not
>>have the meter pulled? While insulation
>>piercing taps are designed for âhot workâ,
>>there use for that should be limited to tapping
>>conductors that have OCP, and arenât under
>>load, with generous working space, like in a
>>piece of switch gear. Even in that situation,
>>making taps on energized conductors should only
>>be done when itâs an absolute necessity.
>>Iâve got a large body of âhot workâ under
>>my belt, both line and load side and will say
>>that face shields and hot gloves saved my butt
>>on several occasions and Iâve got a nice scar
>>on my neck from a molten piece of lug from a
>>main breaker that broke apart while I was
>>tightening up itâs mounting screw. Stuff
>>happens. Itâs always best to play it safe.
>>
>>Michael Morningstar
>>
>>
>>>On May 10, 2016, at 11:04 AM, Chris Mason
>>><<mailto:cometenergysystems at gmail.com>cometenergysystems at gmail.com> wrote:
>>>
>>>This is what we use - we keep a selection in the van for difficult jobs.
>>>
>>>
>>>
>>>Insulation Piercing Connector 2/0-10 AWG
>>>
>>>
>>>
>>>Part #IPCS2001
>>>Insulation Piercing Connector 2/0-10 AWG 2/0-4
>>>Main, 10-14 AWG Tap, Dual Rated AL9CU, Torque Limiting Nut
>>>
>>>On Tue, May 10, 2016 at 1:27 PM, Kirpal
>>>Khalsa <<mailto:solarworks at gmail.com>solarworks at gmail.com>wrote:
>>>Hi Folks,Â
>>>We have a job requiring a supply side
>>>connection. Wondering if anyone could share
>>>some makes and models for connectors
>>>connecting to the wires between a main meter
>>>and the main breakers in the electrical
>>>panel. Ideally it would be able to be done hot. Â
>>>I am also looking into the ConnectDer meter
>>>collar but will have to coordinate with the
>>>utility for that and am looking to keep things simple. Â
>>>Thank you!!!!
>>>
>>>
>>>Sunny Regards,
>>>Kirpal Khalsa
>>>Oregon LRT#25
>>>NABCEP Certified PV Installation Professional
>>>Oregon Solarworks LLC
>>><http://www.oregonsolarworks.com/>www.oregonsolarworks.com
>>><tel:541-299-0402>541-299-0402
>>>
>>>
>>>
>>>
>>>--Â
>>>Chris Mason
>>>NABCEP Certified Solar PV Installer
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160512/82e134ac/attachment.htm>
More information about the RE-Wrenches
mailing list