[RE-wrenches] Outback programing question
Chris Mason
cometenergysystems at gmail.com
Tue May 3 20:12:48 EDT 2016
There's new firmware out today for the MATE3, you should probably try that.
On Wed, Apr 27, 2016 at 8:31 PM, jay <jay.peltz at gmail.com> wrote:
> HI All,
>
> I’ve got a problem that outback tech hasn’t been able to figure out.
>
> off grid system
> mate 3
> quad stacked VFX 3648
>
> The generator is set to specific start/stop daily timer. This works fine.
>
> The client has plenty of solar for the day, and when he runs his generator
> he doesn’t want the chargers to operate.
> OK so just hit charge off, and yes the chargers will turn off.
>
> But next day, genny starts up, and the chargers come back on as well.
>
> Outback says that shouldn’t be happening, but it is.
>
> Anybody have this issue or know of a fix?
>
> Thanks
>
> jay
>
> peltz power
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160503/e989e485/attachment.htm>
More information about the RE-Wrenches
mailing list