Benn, August, etc

         Sorry for omitting a somewhat crucial detail....below these=20
stringers it is a "standard" residential stacked roof with 2X6 rafters=20
on 16" centers with 1/2 " plywood deck. No purlins.  I appreciate the=20
feedback/good ideas.

Bill

Feather River Solar Electric


On 4/29/2016 3:28 PM, August Goers wrote:
>
> Benn,
>
> We=E2=80=99ve done it several ways including putting four 14 x 1.5=E2=80=
=9D TYPE 17=20
> screws per attachment point through the metal and into the 1=E2=80=9D x w=
ood=20
> purlin. The key is that the load path all the way down needs to be=20
> capable of handling the worst case loads. So we had to check that too.=20
> Some racking manufactures such as Unirac have online calculators to=20
> give point loads.
>
> Best, August
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org=20
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of=20
> *Benn Kilburn
> *Sent:* Friday, April 29, 2016 2:17 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Goofy roofing
>
> August, et al;
>
> If the purlins are only 1"x4" or 1"x6" or....1"x anything, are you=20
> only relying on the 1" purlin as the attachment point or are you=20
> hitting the vertical trusses below the purlins?
>
> We are working on a corrugated roof right now and using a Schletter=20
> roof bracket. The name of it escapes me at the moment. Maybe FixT?
>
> We are attaching to purlins which are 2"x6".  I wouldn't think 1"x=20
> anything would provide enough pull-out?
>
> Benn Kilburn
>
> SkyFire Energy Inc.
>
> 780-906-7807
>
>
> On Apr 29, 2016, at 9:09 AM, August Goers <august at luminalt.com=20
> <mailto:august at luminalt.com>> wrote:
>
>     Hi Bill,
>
>     It sounds like you=E2=80=99re talking about a purlin type setup =E2=
=80=93 4=E2=80=99
>     sounds a little far apart but I guess that=E2=80=99s what you have to=
 deal
>     with. If you have a corrugated metal roof, we=E2=80=99ve used S-5
>     CurruBrackets screwed through the metal and into the purlins and
>     then either run the solar rail up and down the roof or install a
>     sub-rack system (with strut or angle aluminum) perpendicular to
>     your solar rail.
>
>     Best,
>
>     August
>
>     *From:*RE-wrenches
>     [mailto:re-wrenches-bounces at lists.re-wrenches.org
>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
>     *frenergy
>     *Sent:* Friday, April 29, 2016 6:55 AM
>     *To:* RE-wrenches
>     *Subject:* [RE-wrenches] Goofy roofing
>
>     Recently, a customer had a metal roof (not standing seam)
>     installed by a "handyman".  Pretty clean installation however for
>     some reason he ran 1X6 stringers across the roof  on the 1/2"
>     plywood deck spaced about every 4 feet (as you go from ridge to
>     eaves).  Of course the roofing screws are at the stringers.  I'm
>     sure he had a /great/ reason for doing so.  So now I have been
>     asked to install an array on this roof.  You can feel how "soft"
>     the roof is as you walk on it of course because you are walking on
>     air-below-metal for most of the roof.  Stringer locations don't
>     jive with possible feet/post locations for rail. I'm usually
>     pretty good at problem solving but I'm accepting ideas.
>
>     Bill
>
>     Feather River Solar Electric
>
>     Bill Battagin, Owner
>
>     4291 Nelson St.
>
>     Taylorsville, CA 95983
>
>     530.284.7849
>
>     CA Lic 874049
>
>     www.frenergy.net <http://www.frenergy.net>
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis=
t.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.o=
rg/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>


--=20
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20160430/23843ead/attachment.htm>


More information about the RE-Wrenches mailing list