[RE-wrenches] Storage Batteries for dwellings -Canadian Code

Chris Mason cometenergysystems at gmail.com
Fri Apr 8 12:04:59 EDT 2016


The Powerwall is an integrated product,  not a battery you install. There
is no user access to the internal voltage. Our Nissan Leaf stores at 500v
but it's not restricted for the same reason. There are plenty of commercial
UPS products that use very high villages but the user had no access to the
internals.
On Apr 8, 2016 1:06 AM, "Benn Kilburn" <benn at skyfireenergy.com> wrote:

> Wrenches,
> Section 64 of the 2015 Canadian Electrical Code covers Renewable Energy
> Systems.
> Rule 64-800(3) states...
>
>    1.
>
>    Storage batteries for dwelling units shall have the cells connected so
>    as to operate at less than 50 V nominal.
>
> Note the word "for".  It appears that this rule may restrict the use of
> higher voltage lithium ion batteries (PowerWall and similar Panasonic home
> storage that i've heard of) FOR dwellings regardless of where it is
> installed (detached or attached garage or even a separate shed)
>
> Based on the short text that i've included, does anyone interpret it
> differently or know of another rule in the CEC that may be a work-around?
>
> For the NEC'ers... i only have a copy of the 2011 NEC and haven't read it
> cover to cover yet ;) but is there a similar rule in there regarding
> storage battery voltage FOR dwellings?
>
> Thanks
>
> *Benn Kilburn *
> CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
> 6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
> P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
> [image: email] <benn at skyfireenergy.com> [image: facebook]
> <https://www.facebook.com/SkyFireEnergy> [image: twitter]
> <https://twitter.com/SkyFireEnergy> [image: linkedin]
> <https://www.linkedin.com/company/283735?trk=tyah&trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5>
>  [image: google] <https://plus.google.com/+SkyFireEnergy/>
>
> [image: SkyFire Energy Logo_horizontal]
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160408/bc98dc3d/attachment.htm>


More information about the RE-Wrenches mailing list