[RE-wrenches] Specific AC Coupling question

Mac Lewis maclewis1 at gmail.com
Thu Apr 7 09:41:41 EDT 2016


Hi Allen,

Another thing that you may want to talk with Schnieder about is if the "max
sell" about applies if there is AC coupling is involved.  I believe that
the max sell amps is talking about how much the XW+ can pull off the DC
buss, not necessarily how much will flow to the main service through its
terminals via AC coupling.  It may not be a bottleneck in your case.

Good Luck

On Tue, Apr 5, 2016 at 3:13 PM, Jeremy Rodriguez <allsolarjeremy at msn.com>
wrote:

> Have installed a 5548 and 6048 XW with  IG Plus 10.0 with fair results.
> On/Off when AC coupled during the test phase. I have not heard any
> complaints from the homeowner.
>
> Jeremy Rodriguez
> Solar Installation And Design Expert
> All Solar, Inc.
> 1463 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand!
>
> On Apr 4, 2016, at 1:34 PM, Allan Sindelar <allan at sindelarsolar.com>
> wrote:
>
> Wrenches,
> Core question first: Will a ~2010 Fronius IG-4000 respond properly to the
> frequency shift regulation supplied by a new Schneider XW+5548 or XW+6848?
>
> Situation: I haven't seen the Colorado site; I'm working as a consultant
> to produce an upgrade component list and will later serve as a resource
> during local installation of the upgrade equipment. Customer has hired me
> to turn a hodgepodge system into a GTBB system. The system has two key
> parts: an existing SW5548 with batteries, never properly installed (only
> AC1 in was ever connected to a main load center!) with 3.1 kW of
> tracker-mounted PV through an Outback FM60; and a roof-mounted 4kW array
> feeding the grid panel via the IG-4000. As currently installed, nothing
> will operate as wired during a grid outage, and a 240V AC well pump isn't
> supported.
>
> The simple plan is to replace the SW5548 with an XW+5548 or 6848 with
> Midnite E-Panel; replace batteries with Surrette FLAs; keep existing arrays
> unchanged; use existing FM60 for smaller tracked array; use existing
> Fronius IG-4000 but AC couple it to the output of the XW. The customer
> understands that sell amperage is limited by the inverter (to 20A @ 240V
> for the 5548, or 4,800W, or 27A @ 240V for the 6848, or 6,480W) when the
> grid is up, but the full array can charge the battery bank when the grid is
> down.
>
> Schneider tech support assures me that the XW+ is good in this
> application, but I need to get an OK from Fronius about frequency-shift
> compatibility. Fronius tech support tells me that it may or may not work:
> the 0.4 hz shift is within the the normal frequency tolerance for this
> model. While the tolerance window may be tightened up in the field, such
> tightening may cause nuisance tripping, especially with reactive loads like
> a well pump or A/C. The tech suggested that we first test the
> frequency-shift approach, and add a DC-coil contactor between the output of
> the Fronius and the XW+ if it doesn't.
>
> Has anyone AC coupled these two units? Did it work? Any unexpected
> problems? Did you add a voltage-controlled contactor? What should I advise
> my client?
> Thank you,
> Allan
> --
>
> *Allan Sindelar*
> <allan at sindelarsolar.com>allan at sindelarsolar.com
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> *505 780-2738 <505%20780-2738> cell*
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160407/edf4b834/attachment.htm>


More information about the RE-Wrenches mailing list