[RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

Glenn Burt glenn.burt at glbcc.com
Wed Mar 2 13:53:31 EST 2016


I believe that John Wiles has stated this in a couple of places in print, therefore you may have a tough time justifying a way around the rule to an AHJ.

Supply side connections are very popular in this situation.

-----Original Message-----
From: "August Goers" <august at luminalt.com>
Sent: ‎3/‎2/‎2016 11:32
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for	center-fed panelboards

All –



We are seeing more AHJs not allowing us to use the NEC 7015.12(D)(2)(3)(b)
120% rule on center-fed panelboards. For example, if we have a 100 A
meter/main combo with a center fed 100 A breaker we cannot apply the 120%
rule at all and need to do a panel swap. What are other wrenches doing in
this case?



Best,



August

Luminalt
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160302/3f2e49a1/attachment.htm>


More information about the RE-Wrenches mailing list