[RE-wrenches] Shading from Overhead Transmission Lines
Jerry Shafer
jerrysgarage01 at gmail.com
Wed Feb 24 18:08:12 EST 2016
Just so l understand you had current not voltage where was the current
flowing to.
I have had static voltage from HV transmission lines but not induced
current while the system was off.
Jerry
Jerry
On Feb 24, 2016 12:42 PM, "Rebekah Hren" <rebekah.hren at gmail.com> wrote:
> I'd be more worried about induced current/voltage on metal/conductors in
> the PV array, which seems like it could cause issues with GFP devices, and
> possibly unsafe conditions. I worked on one large array (5 MW) where the
> point of interconnection was parallel to / under high voltage lines. Even
> when the PV system wasn't operating there was measurable current on the PV
> system conductors induced from the high voltage lines above. The utility
> nearly wouldn't let the system be allowed to interconnect, because we had
> trouble proving the anti-islanding was working as current was still flowing
> when the utility supply was disconnected (on the lower voltage not higher
> voltage lines).
> Rebekah
>
>
> On Wed, Feb 24, 2016 at 4:18 PM, Jerry Shafer <jerrysgarage01 at gmail.com>
> wrote:
>
>> We have both GT and off grid in the shadow lines, because of the distance
>> away, diameter of the wire and also the sun have not seen any issues that
>> will warrent micro inverters. All that said, its a moving target and if the
>> wires are very close then it will be more of an issue.
>> Something else to ponder can you in fact install under HV transmission
>> lines in your area.
>> Jerry
>> On Feb 24, 2016 5:50 AM, "Paul Lyons" <Lyons at zapotecenergy.com> wrote:
>>
>>> Hell RE-Wrenches –
>>>
>>>
>>>
>>> Do any of you have experience with locating ground-mounted PV systems
>>> under high-voltage transmission lines? We have an electric utility client
>>> who would like to use some of its land underneath its HV transmission lines
>>> to install PV. Is the shadow cast be the overhead wires significant enough
>>> to affect the string voltages in the array? Should we go with
>>> micro-inverters?
>>>
>>>
>>>
>>> Thank you,
>>>
>>>
>>>
>>> Paul Lyons, P.E.
>>>
>>> Zapotec Energy Inc.
>>>
>>> 675 Massachusetts Ave
>>>
>>> Cambridge, MA 02139-3309
>>>
>>> Tel: 617-547-5900 ext.201
>>>
>>> Email: Lyons at ZapotecEnergy.com
>>>
>>> Web: www.ZapotecEnergy.com
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Tel: 336.266.8800
> NABCEP Certified Solar PV Installation Professionalâ„¢ 091209-85
> NC Licensed Electrical Contractor
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160224/961d71f0/attachment.htm>
More information about the RE-Wrenches
mailing list