[RE-wrenches] Aquion Batteries

Dan Fink danbob88 at gmail.com
Fri Jan 29 13:52:24 EST 2016


I second Larry's concerns about Aquion's SOC/voltage curves and tripping
LVD at only 40% DOD with standard PV equipment, tied in with not being able
to handle high discharge C-rates and surge loads. I did some math on
running a typical off-grid home with a well pump on Aquions, and it wasn't
pretty, but I may not have done the math right. Very interested to hear
personal experience on off-grid homes with these batteries.

 I was starting to envision applications for remote MET tower, repeater
tower etc applications with low discharge C-rates and high charging
C-rates, and then saw Aquions lowest operation temperature of -5C, 23 F.
That's considered a "heat wave" during certain times of year in many areas,
including here in sunny Colorado. In these applications the batteries are
NOT in a heated room, instead an outdoor enclosure at the base of a tower.

AGMs are serving us here just fine on these sorts of esoteric
installations, and they have no problem with -29C and lower when kept at
high SOC. And, cheap, easy to replace, and giving us many years of life.
The ROI math on the Aquions compared to AGM is not adding up for me on
these applications.

My only experience with Aquion was their class at the NABCEP conference
last year.

Any ground truth experience and stories on Aquions and other similar
technologies appreciated here also.

Best regards;

Dan Fink
Adjunct Professor, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Accredited Continuing Education Providers™
970.672.4342



On Fri, Jan 29, 2016 at 7:55 AM, Starlight Solar Power Systems <
larry at starlightsolar.com> wrote:

> I too am interested in anyone that has installed these. I had some
> concerns back on Nov 10, 2014. Here is a copy/past from that conversation:
>
> Something does not add up to me. The cell has a voltage discharge curve
> way outside that of RE equipment, 1.75 Vpc down to 0.5Vpc. I can't see how
> this technology could be scaled to RE applications without wasting much of
> the capacity. From what I see, only about 40% could be used before LVD.
>
> And this:
> The Aquion battery claims their 2.4kWh, 48 volt stack operates from 59 to
> 30 volts. Many inverters have a LBCO of 1.75 Vpc (42 volts). Depending on
> voltage sag, that means about half of the capacity of the Aquion battery
> can't be used. Even if the outback can operate down to 1.5 Vpc, you are
> still not able to use the full capacity of the battery unless your load is
> less than 800 Watts.
>
> I have reviewed their technical presentation and it looks to me like the
> capacity simply can't be used in the off grid environment. If you can't use
> it, why do they rate it at 2.4kWh? BTW, the Voltage vs.Energy chart on the
> spec sheet does not match the first chart I posted.
>
>
>
>
>
>
>
> On Jan 29, 2016, at 7:30 AM, Chris Schaefer <chris at solarandwindfx.com>
> wrote:
>
> To All,
>             Great insight on the lithium movement. I do am looking for
> anyone dealing with the new Aquion batteries. I’ve got a couple of
> potential clients that have inquired about them. Saw them at a NABCEP
> training session last spring and while the idea is moving I wasn’t
> impressed. Perhaps it’s time to start a new thread, “Aquion batteries”.
>
> Thanks,
> Christopher
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of *
> don at energysolarnow.com
> *Sent:* Friday, 29 January, 2016 00:49
> *To:* Dan Fink
> *Cc:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] LiFePO4; WAS Availability of Powerwall
> Batteries
>
> Thanks for sharing your experience with these batteries, Dan.
> I have similar SOC issues with an off-grid customer who has the Aquion
> Hybrid Ion batteries.
> It has difficulty reaching full charge from solar, requiring the genny to
> kick on each morning even in the summer.
> This is even worse in cold winter weather.
> Your explanation of the change in Peukert's exponent above 80% SOC with
> NiFe batteries sounds like what is happening here as well.
> Do you have any experience with Aquion batteries that you can share?
>
> Thanks
> Don Barch
> Energy Solar
> don at energysolarnow.com
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160129/19470bfd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: egcjjhdh..png
Type: image/png
Size: 71704 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160129/19470bfd/attachment.png>


More information about the RE-Wrenches mailing list