the communication cable IS required, to switch the Sunny Boys
from grid tie to off-grid mode, in the event of a grid failure. 
This is true for the older SB U series, while one is able to move the rotary switch on the TL series of inverters. This grid/off grid setting is also able to be adjusted using the SMA service tool. This Off Grid mode set in the SB inverters can only be used when using a SI as now the SI is meeting the anti island mode for any grid tied system.
Com cable is used between the SI & the SB for the web box & sunny sensor box. 

On Jan 16, 2016, at 1:30 PM, Richard L Ratico wrote:

> All,
> 
> I've just updated the inverter firmware (to version 7.302) in an off-grid
> 120/240 Volt split phase Sunny Island, generator only system I installed in
> 2007. It's my understanding the Sunny Islands DO need an external shunt if if
> there are any DC loads or charging sources. I don't have any of those, other
> than battery vent fans, but installed a shunt anyway to work with a Trimetric.
> 
> Furthermore, In an off-grid install, the Sunny Islands control Sunny Boy
> inverters (which are pre-programmed for off-grid use) by frequency shifting
> alone, no separate communication cable is required. In a grid-tie, battery
> backup situation, the communication cable IS required, to switch the Sunny Boys
> from grid tie to off-grid mode, in the event of a grid failure. 
> 
> Dick Ratico
> Solarwind Electric
> 
> 
> --- You wrote:
> Hi Mark,
> 
> If all battery power flows in and out of Sunny Island(s) then it will keep
> track of SOC without a external shunt. I'm not sure how it does it but all
> the SOC dependent controls work fine in that scenario. The SOC algorithm
> calculation works much better than any other that I've used.
> On Jan 16, 2016 1:34 PM, "Mark Frye" <markf at berkeleysolar.com> wrote:
> 
>> Folks,
>> 
>> I know with both the Radian and the SI you can use an external shunt to
>> support the measurement of KWH and support various SOC controls.
>> 
>> But what happens if you don't use an external shunt?
>> 
>> I am pretty sure that the Radian does not have an internal shunt to
>> support SOC control.
>> 
>> What about with the SI? Does it implement it's SOC controls even without
>> an external shunt?
>> 
>> Thanks,
>> 
>> Mark Frye
>> Berkeley Solar Electric Systems
>> 
> --- end of quote ---
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> Tump at swnl.net               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                              
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20160118/2238437f/attachment.htm>


More information about the RE-Wrenches mailing list