Dellta LA lightning arrestors would not prevent the diode damage you=20
mentioned. I think many others on the list will confirm that Delta LAs=20
are not effective at preventing equipment damage, and probably only=20
useful in preventing complete wire melt down. Midnite found the Delta=20
didn't start clamping till well over 2000 volts. It might be=20
coincidence, but we have not a single case of lightning damage since we=20
switched to the Midnite SPD protection. The Delta isn't even UL listed=20
anymore.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 11/29/2015 1:08 PM, Starlight Solar Power Systems wrote:
> I concur with your =E2=80=9CWow=E2=80=9D comment about Panasonic performa=
nce. I have=20
> never found any module to outperform them except for Uni-Solar. It=E2=80=
=99s=20
> sad that both products are no longer available.
>
> Larry
>
>
> On Nov 27, 2015, at 4:02 PM, Chris Worcester <chris at solarwindworks.com=20
> <mailto:chris at solarwindworks.com>> wrote:
>
> Hi Friends,
> We did a run of Sanyo modules for a few years. Last year one of our=20
> HIT 195 BA3 arrays of 12 started losing production, a 2005 system with=20
> the fabled SMA SB2500U. the warranty process was really intense, a lot=20
> of photos per module required, and much documentation. To no avail, as=20
> Panasonic came back with the science showing how lightning took out=20
> the blocking diodes at various degrees through the years? We had this=20
> well-grounded, 600 VDC RK5 fused, Delta LA DC602, and more. So in the=20
> end we asked the client to see if the homeowner=E2=80=99s insurance might=
come=20
> forth. Yes they did! We just replaced the array with Panasonic HIP=20
> 240=E2=80=99s and Apsystems YC500 micro inverters, wow! This system rips,=
=20
> showing 270 watts per module in our cold climate! The Panasonic=E2=80=99s=
were=20
> acquired from CivicSolar, good people to work with!
> Happy Holiday! There is lots to be grateful for.
> Chris Worcester
> Solar Wind Works
> NABCEP Certified PV Installer
> Office 530-582-4503
> Cell 530-448-9692
> Fax 530-582-4603
> www.solarwindworks.com <http://www.solarwindworks.com>
> chris at solarwindworks.com <mailto:chris at solarwindworks.com>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]=20
> *On Behalf Of *Starlight Solar Power Systems
> *Sent:* Friday, November 27, 2015 12:47 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Panasonic PV modules, missing you
> Has anyone been able to purchase Panasonic modules in the US in the=20
> last few years? If so, where?
>
> Thank you,
>
> Larry
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.o=
rg/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.=
org/attachments/20151129/6e524356/attachment.htm>
More information about the RE-Wrenches
mailing list