[RE-wrenches] Odd battery problem - very low SG in only one cell
Bill Loesch
solar1online at charter.net
Mon Nov 23 06:57:05 EST 2015
Hi Dan,
No definitive suggestions, but kudos for making it a learning experience
for _all_. Great analytical technique. Hopefully you gain more
credibility with the kids as a result of your candor.
Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094
On 11/22/2015 8:49 AM, Dan Fink wrote:
> Esteemed Wrenches;
>
> I'm looking for input on what could be going on with a battery bank at
> the college I teach for. It's a stand-alone system with 4 Trojan 12v
> T-1275 in series / parallel for 24v, 660w of PV, running only a
> drainback solar hot water system for space heating. So, 3 pumps and 3
> DTCs, max load 100 watts and doesn't run all that often, outback CC is
> usually in float. The batteries are only 2.5 years old and are
> regularly maintained.
>
> My lab class tested and maintained the battery bank last week, and on
> one battery there was one cell, in the middle of the battery, with a
> SG so low it wouldn't even register on our refractometer or midnite
> hydrometer. That battery reads about 0.2v lower than the others. All
> the other cells in that battery read reasonable SG, with 2 cells on
> the downstream side reading SG slightly low, but still in reasonable
> range. This was of course all before topping up the electrolyte with
> distilled water.
>
> Our troubleshooting exercise looked at:
> ~ Measurement error? Nope, I was right there supervising and 2
> different lab classes got the same results with 2 different instruments;
> ~ Stratification? A suspicion especially since the system is usually
> in float. We equalized twice, no change in SG. I DID hear that likely
> this was the first time the batteries had ever been equalized, but no
> way to know for sure.
> ~ Spilled electrolyte from tipped battery replaced with water by a
> previous instructor's class? Can't see this, all the other cells would
> have lost electrolyte too;
> ~ A student accidentally discharged electrolyte into the bucket
> instead of back in the cell, then was replaced by distilled water when
> topping up? I can't see that either, the midnite hydrometer needs only
> a small sample.
>
> So, I'm left with "likely we have a cell that is failing for some
> reason" and students secretly smug that the professor is also stumped.
>
> Any ideas?
>
>
> Dan Fink
> Adjunct Professor, Ecotech Institute
> IREC Certified Instructorâ„¢ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Accredited Continuing Education Providersâ„¢
> 970.672.4342 <tel:970.672.4342>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20151123/7bbd5bd2/attachment.htm>
More information about the RE-Wrenches
mailing list