[RE-wrenches] Classic 150 100 amp output breaker tripping?????
boB at midnitesolar.com
boB at midnitesolar.com
Fri Nov 6 21:13:12 EST 2015
I might take a clamp on ammeter and check the Classic's battery side
current.
Then maybe turn ON the generator and see what happens to the current
on that line.
boB
On 11/6/2015 1:49 PM, Daniel Tittmann wrote:
> there is a MNSPD 300 AC and a MNSPD 300 DC. are wired into the system.
>
> this is a new system. Has been happening since commissioning.
> it is possible that the generator is charging during those morning
> hours as there are likely morning loads, coffee pot, but not always as
> the customer just went on vacation and the breaker tripped while he
> was gone.
>
> On my first return visit I re routed the controller battery + from the
> battery + buss bar to the battery + on the battery bank itself as this
> had solved an similar issue in the past.
>
> So for tomorrow's visit I am planning on taking a new breaker and a
> new controller. Is there anything else that I should replace?
>
> Daniel Tittmann
> CTO
> Greenwired
> www.greenwired.com <http://www.greenwired.com>
> daniel at greenwired.com <mailto:daniel at greenwired.com>
> 707-923-2001 (office)
> 707-206-5088 (Cell)
>
> On Thu, Oct 29, 2015 at 4:19 PM, boB at midnitesolar.com
> <mailto:boB at midnitesolar.com> <boB at midnitesolar.com
> <mailto:boB at midnitesolar.com>> wrote:
>
>
> Larry, because these MPPT CC's are bi-directional (for
> efficiencies' sake), they can convert a large current
> at the battery side to a smaller current at the PV side if not
> adjusted right. Normally this is just taken
> care of and reduced to a bare minimum by the controller watching
> the voltages and currents carefully.
> It is technically possible though for things to not work exactly
> correctly. I am not saying that this is
> for sure happening, but it is possible. The ramping up in
> battery voltage from the chargers should
> be plenty slow enough for this not to be a problem but I am wildly
> speculating that this could happen
> and cannot rule it out. There may of course be something else
> completely different happening here
> though.
>
> If CBI breakers are being used, these are known to be extremely
> fast at tripping when overloaded.
>
> Also, what, if any SPDs are connected to the system ?
>
> boB
>
>
> On 10/29/2015 2:45 PM, Starlight Solar Power Systems wrote:
>> After the Magnum Inverter/charger samples incoming AC power, they
>> have a slight delay before starting the charger. Then, they ramp
>> up current slowly.
>>
>> Even so, how will any current from any other source pass through
>> the breaker unless the Classic is presenting a load? I suppose
>> something else could be wired through the breaker but I’m
>> guessing Daniel would have looked at that.
>>
>
> <<<Curious Larry's PICTURE GOES HERE>>>
>
>> Curious Larry
>>
>>
>> On Oct 29, 2015, at 1:06 PM, boB at midnitesolar.com
>> <mailto:boB at midnitesolar.com> wrote:
>>
>>
>> ...if it turns out to be, say, a surge in battery voltage from
>> the generator
>> starting up and causing a reverse current through the battery
>> terminals…
>>
>> boB
>>
>>
>>
>
>
> ____
>