[RE-wrenches] Combined Inverter Fuse sizing

Jason Szumlanski jason at floridasolardesigngroup.com
Sat Oct 24 18:27:34 EDT 2015


Clarification - it's square root of 3, not 2, and if the Inverter Output
Current is specified on a datasheet for a 3-phase inverter, it would
already have the factor applied and that is the rating used to apply to
1.25x factor.

For example, Sunny Tripower 12,000 has a inverter output rating of:

12000 / 480 / sqrt(3) = 14.43 (listed as 14.5). Multiply the number of
inverters times 14.5 times 1.25 to get the combined OCPD and wire rating
required.



On Sat, Oct 24, 2015 at 8:39 AM, Glenn Burt <glenn.burt at glbcc.com> wrote:

> Two things,
> Combined OCPD sizing is based on the output current of the inverters, not
> the individual OCPD values.
> And in most 3 phase systems you will have a square root of 2 to factor
> into your calculations.
>
> Sincerely,
> Glenn Burt
> Sent from my 'smart' phone so please excuse grammar and typos.
> ------------------------------
> From: Allen Frishman <amfrish at aeonsolar.com>
> Sent: ‎10/‎24/‎2015 7:50
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Combined Inverter Fuse sizing
>
> Wrencher's,
> Quick question regarding sizing the fuse for a combined group of
> inverters.   If I have six 10KW three phase inverters each with a max AC
> current of 30A they each require a 3 pole 40 A breaker.   If I then take
> the combined output of the AC combiner panel I see two possible options for
> sizing the combined fuse size.
>
> 6 inverters x 40A breakers each = 240A so I need to use a 250A fuse
> 6 Inverters x 30A max output each = 180A x 1.25 = 225A Fuse
>
> Seems like both are acceptable options since all wire will be protected.
>
> All feedback is appreciated.
>
> *Al Frishman*
> AeonSolar
>
> *(917) 699-6641 <%28917%29%20699-6641> - cell*
> *(888) 460-2867 <%28888%29%20460-2867>*
> *www.aeonsolar.com <http://www.aeonsolar.com/>*
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20151024/bde115a6/attachment.htm>