[RE-wrenches] Combined Inverter Fuse sizing
Allen Frishman
amfrish at aeonsolar.com
Sat Oct 24 07:50:38 EDT 2015
Wrencher's,
Quick question regarding sizing the fuse for a combined group of inverters. If I have six 10KW three phase inverters each with a max AC current of 30A they each require a 3 pole 40 A breaker. If I then take the combined output of the AC combiner panel I see two possible options for sizing the combined fuse size.
6 inverters x 40A breakers each = 240A so I need to use a 250A fuse
6 Inverters x 30A max output each = 180A x 1.25 = 225A Fuse
Seems like both are acceptable options since all wire will be protected.
All feedback is appreciated.
Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20151024/8947b2f7/attachment.htm>
More information about the RE-Wrenches
mailing list