[RE-wrenches] Rapid Shutdown Battery Systems
billbrooks7 at sbcglobal.net
billbrooks7 at sbcglobal.net
Thu Aug 27 00:19:34 EDT 2015
Ray,
Do you have a massive battery bank and 3, 8kW inverters inside the house? Is
this in a garage or power shed. If it is a power shed, then 690.12 is not
intended to relate to the power shed. That will be clarified in the 2017
NEC.
The area for discussion is what constitutes the length of battery cables.
690.71 has restrictions on where overcurrent protection needs to be for
circuits longer than 5'. Do people really follow that religiously? This
would be a discussion that really needs to happen with the AHJ. My basic
view is that if I have a 4' run from a battery box to my inverters (even
though one lead may be 10' long), many would call that a 4' run. That is
what is exposed from a fire fighter point of view. Remember the battery is
potentially a massive bomb in a fire, so 48V conductors are the least of a
fire fighter's concern.
Bottom line is how to make it easy for a firefighter to kill the vast
majority of wires in a building. A backup system simply reenergizes
everything. Cutting off the dc from the array and the ac out of the
inverters solves the problem--keep the battery as close as possible and
don't worry about trying to turn off the battery circuit to the inverter.
Bill.
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Ray Walters
Sent: Wednesday, August 26, 2015 12:40 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Rapid Shutdown Battery Systems
Hi Wrenches;
I have an upcoming project to be inspected, ,and having spent too much time
on off grid and out of country work, I'm now playing catch up with the new
690.12 and 690.71(H) requirements.
The proposed GTB system is 3 Radians with a ground mounted 18kW array and
large HUP battery bank. I just read a Bill Brooks article that basically
says that Rapid Shutdown not only applies to ground mounted arrays that come
into buildings, but also applies to battery cables if longer than 5 ft.
There are 690.12 compliant combiners from Midnite that work with their
Birdhouse system, so I think I've got a handle on the array requirements
(more or less).
What is stumping me is how to feed three 8kW inverters from a large battery,
and install auto disconnect breakers within 5 ft.
1) the disconnect has to be large enough, Midnite only makes a 250 amp
remote trip breaker, so I'd have to parallel 3 of these?
2) 690.71(H)3 says the breaker can't be in the battery enclosure, which is
tricky since the enclosure is 160" long from one end to the other with 2
parallel strings.
3) I'm having trouble even finding an enclosure for 3 large DC breakers
(Flex 1000 is the only thing I know of) and to get the enclosure close
enough is an issue too.
I just got off the phone with Tech support at Outback and they don't seem to
have any Rapid Shutdown gear ready.
Are inspectors actually requiring this yet, or because of the lack of
available UL listed products, can we take a pass on at least some of the
requirements? Another strategy the Outback tech thought of is to put all
the equipment into a shipping container and then its not in or on a
"building", and 690.12 doesn't apply.
--
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
More information about the RE-Wrenches
mailing list