[RE-wrenches] wiring methods between arrays
Benn Kilburn
benn at skyfireenergy.com
Wed Aug 12 10:32:48 EDT 2015
If you have attic access between the two roofs or separated arrays then install a Soladeck at each array and run the interconnecting wires thru the attic. If it is a DC circuit then Teck cable, or AC90 would be my choice of (armoured) cable for running through the attic.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Aug 11, 2015, at 3:19 PM, August Goers <august at luminalt.com> wrote:
>
> Hi Wrenches,
>
> I have another best practices questions: what are you doing to run your PV wire between arrays on a rooftops? This question has come up on this list in the past but I’m still on the hunt for a robust and faster lower cost method. We mostly install outdoor boxes on each sub array and then run EMT between these boxes. We use strain reliefs to enter the boxes and then either keep PV wire or transition to THWN-2 in the EMT depending on the layout. This method takes time and the outdoor boxes aren’t cheap. Alternatively, we can run open-ended EMT with ground bushings on the ends to bond the conduit. Since ground bushings are designed to be used in boxes we switch out the aluminum lug with a tin-coated outdoor rated lug and stainless hardware. This technically violates the listing but at least the materials hold up. The EMT needs to be carefully bent down at the ends so rain doesn’t enter. Lastly, we sometimes run our PV wires along strut or angle aluminum (this is the fastest method) which also needs to be bonded with a lay-in lug.
>
> Does anyone have other methods?
>
> Best,
>
> August
> Luminalt
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150812/a7402b9d/attachment.htm>
More information about the RE-Wrenches
mailing list