[RE-wrenches] Iron Edison Batteries
Jay
jay.peltz at gmail.com
Mon Jul 27 10:47:07 EDT 2015
Hi dan
I'm curious why you opted for NiFe vs lithium?
Jay
Peltz power.
> On Jul 26, 2015, at 8:11 PM, Dan Fink <danbob88 at gmail.com> wrote:
>
> I made myself a guinea pig on Iron Edison NiFe cells this year, before I try to install them for any customer. I have now about 90 days on them.
> 1.65 volts per cell charging is what they want and need. PV controllers MPPT type are fine with this. just change the settings (assuming the sun is shining)
> . Inverter/chargers are not fine, at least not my Magnum OMG! over 1.6v per cell!! Overvoltage! Shut down!
> So I have rewired battery bank as recommended by Mrf with 9 cells at 1.2v instead of 10 cells. And now with my 10.8v battery bank I get surge low voltage wonky waveform hits from the fridge turning on, etc. that reboot the satellite internet, tv etc.
> My plan is to add another 1kw of solar here for an increase of 50% and rely more on the incoming PV that can bring it all up to 1.65v per cell rather than the generator that can't do it thanks to the inverter firmware.
> I think my new NiFe batteries will do just great in the long run. But their charge/discharge behavior is a continuing lesson. And I am SO glad to learn these lessons myself, instead of in front of a critical customer.
>
>
>
> Dan Fink
> Buckville Energy
> IREC Certified Instructor™ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP / IREC / ISPQ Accredited Continuing Education Providers™
> 970.672.4342
>
>
>
>> On Sun, Jul 26, 2015 at 6:55 PM, jay <jay.peltz at gmail.com> wrote:
>> HI Tom,
>>
>> They are considered 1.2v nominal.
>>
>> Charge range is up to 1.7v per cell.
>> For a 24v system usually you pull out 1 cell or 19 cells 19 x 1.7 = 32.3v
>> For a 48, usually 2 or 3 , or 37-38 cells.
>>
>> If you use much less, then the voltage swings really low, if you go more the voltage is too high for most inverters.
>> The Iota isn’t going to charge them up fully with that low a voltage. But I don’t know if that version Iota is adjustable, many of the older ones had a internal pot you could turn up.
>>
>> But heck give it a try and play with it.
>>
>> jay
>>
>> peltz power
>>
>>
>>
>>
>> > On Jul 26, 2015, at 4:34 PM, Tom Lane <tom at ecs-solar.com> wrote:
>> >
>> > I have a friend who has forty ( 40 ) Iron Edison Batteries , he says they are each 1.5 volts and wants to use them for a backup to his aquatics business's . Continuous load 24/7 is only 365 watts with surges to 1200 watts . My guess is that ___# of batteries ( maybe 32 to 36 ? ) can be wire as a 48 volt system ? Any suggestion on charge controllers - Morningstar or MidNite ? . .? A Samplex pure sign wave inverter 2000 watts at 48 volts and an Iota 54 volt battery charger is my guess that it might be the way to power the load - any suggestions . Anyone have experience with Iron Edison .any suggestions appreciated ! Gator tom PS : any suggested websites ?
>> >
>> > Sent from my iPad
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150727/3e605c48/attachment.htm>