[RE-wrenches] Rapid Shutdown

Mac Lewis maclewis1 at gmail.com
Fri Jul 17 15:14:35 EDT 2015


Hey Steve,

Yes I'm reading that code article closely and I think its open to
interpretation.  If you consider PV circuits to include the battery based
inverters, you would need to include them in rapid shutdown.

 For some reason I thought it applied to all of the DC conductors,
including the battery cabling, but it looks like that isn't explicitly
called out.  Midnites system does have a way to do it..  That will probably
show up on the next code cycle.

Thanks for pointing that out.

On Fri, Jul 17, 2015 at 11:30 AM, Steve Jefferson <
Steve.Jefferson at sma-america.com> wrote:

>  Mac,
>
>
>
> Do you mean to ask for a way to shut down the Sunny Boys connected to the
> Multicluster box?
>
> Sunny Islands are not applicable to the rapid shutdown requirements. They
> are not PV.
>
>
>
> SMA America, LLC
>
> Steve Jefferson
>
> Service Line Supervisor
>
> 3925 Atherton Ave
>
> Rocklin, CA 95765 - 3714
>
> U.S.A.
>
> Tel:  +1 916 625 3185 (direct)
>
> Fax: +1 916 625 0871
>
> Mobile: +1 916 622 4253
>
> Email: Steve.jefferson at SMA-America.com
>
> www.SMA-America.com <http://www.sma-america.com/>
>
>
>
> [image: cid:image001.png at 01CF1CFA.FE18BEB0]
> <http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be>
>
>
>
> This email and any attachments thereto may contain SMA America, LLC
> confidential, privileged and private material for the sole use of the
> intended recipient. Any review, copying, or distribution of this email (or
> any attachments thereto) by others is strictly prohibited. If you are not
> the intended recipient, please contact the sender immediately and
> permanently delete the original and any copies of this email and any
> attachments thereto. Thank you.
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Mac Lewis
> *Sent:* Friday, July 17, 2015 10:27 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Rapid Shutdown
>
>
>
> Hi Wrenches,
>
>
>
> I am working on a rapid shutdown design with an SMA multi-cluster box with
> 6 x 6048 Sunny Island Inverters, 2 per phase.  I will be utilizing a
> Midnite system for some roof top combiners.  Is there a way to shutdown the
> Sunny Islands via communication from the Midnite rapid shut down box?  Or
> do I need to do shunt-trip breakering?
>
>
>
> Thanks
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150717/bf60e77c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 30736 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150717/bf60e77c/attachment.png>


More information about the RE-Wrenches mailing list