The reason behind this rule, going back through some history, was to
reduce the possibility of a nail penetrating hidden conduit (conduit
behind a wall). Since the conduit is exposed/visible, the chances of
that action happening are small to none. So, the installer is saying
that a literal interpretation is not consistent with the intent of the
NEC. May have to ask the AHJ for their position.
On 7/13/2015 1:01 PM, Dana wrote:
> Your assumption is the rule here. Metal inside a building envelope and it cannot transition at the penetration it must be metal before entry.
>
> ----------------------------------------------------------------------------
> Dana Orzel
> Great Solar Works, Inc - NABCEP # 051112-136
> E - dana at solarwork.com - Web - solarwork.com
> O - 970.626.5253 C - 208.721.7003
> "Responsible Technologies for Responsible People since 1988"
> Please consider the environment before printing this email.
>
>
>
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Christopher Warfel
> Sent: Monday, July 13, 2015 10:59 AM
> To: re-wrenches at lists.re-wrenches.org
> Subject: [RE-wrenches] DC conductors in metallic raceway/conduit
>
> I was under the assumption that dc conductors could only be run inside a building when in metallic raceway/conduit (up to a readily accessible
> disconnect switch) . The building being occupied/residence. A
> contractor ran 5 feet of pvc from the wall penetration to the charge controller in a concrete block garage. I don't see anything that allows this by what I find in the NEC. Has anyone have a reference that permits this? Thank you for any assistance.
>
>
>
> --
> Christopher Warfel, President
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150717/d0778bf6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/x-vcard
Size: 100 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150717/d0778bf6/attachment.vcf>
More information about the RE-Wrenches
mailing list