[RE-wrenches] DC conductors in metallic raceway/conduit
Christopher Warfel
cwarfel at entech-engineering.com
Mon Jul 13 12:58:40 EDT 2015
I was under the assumption that dc conductors could only be run inside a
building when in metallic raceway/conduit (up to a readily accessible
disconnect switch) . The building being occupied/residence. A
contractor ran 5 feet of pvc from the wall penetration to the charge
controller in a concrete block garage. I don't see anything that allows
this by what I find in the NEC. Has anyone have a reference that permits
this? Thank you for any assistance.
--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/x-vcard
Size: 100 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150713/83026d5a/attachment.vcf>
More information about the RE-Wrenches
mailing list