Hi:
I'm not sure how much trouble this has caused, so that's why I asked the
question. With large battery banks, it is possible to end up with a
cabling layout which has a potentially very large loop area as was the
case at one of the sites where I saw problems. Here's a picture of the
battery bank they had created.
The + and - cables were not run side by side and the rack is made out of
steel. The inverters did not like it until we ran the cables along the
battery bank and then side by side. Once that was done, things worked as
expected.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Xantrex Brand | CANADA |
Sales Application Engineer
Phone: +604-422-2528 | Tech Support: 800-670-0707 | Mobile:
+604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.Xantrex.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From:
Ray Walters <ray at solarray.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>,
Date:
06/29/2015 03:05 PM
Subject:
Re: [RE-wrenches] Battery Bank to Inverter Wiring
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
This is fascinating because while I knew the DC cables had an AC
component, I never realized how much inductance played in the volt drop to
the inverter. Thanks for bringing this to our attention Jarmo.
Which brings up another question based on Benn's question: isn't the
battery itself part of the inductive loop? and would the lead inside and
steel cases act to increase the inductance? Should we consider changing
battery layouts not just to shorten cable lengths, but to counter
inductance in the batteries themselves? If needed, we could actually wire
the batteries to "twist" by putting every other 2 v cell in the opposite
row.
My guess is that it wouldn't be worth it, but I've been wrong many
times.......
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 6/29/2015 3:55 PM, Benn Kilburn wrote:
What about when you have the (+) and (-) terminals at opposite ends of a
larger battery bank? Sure you can run the conductors side-by-side once
they meet up on their way to the inverter, but would you consider the
distance between the end terminals a "large loop"?
Ideally the battery string is laid out so the end terminals are close
together and close to the inverter, but this isn't always the case.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
On Jun 29, 2015, at 10:28 AM, Jarmo.Venalainen at schneider-electric.com
wrote:
Hi:
>From the comments so far, it appears that within the wrenches group, good
practices are the rule and DC cables are kept side by side, so the problem
I mentioned hasn't come up much.
I have seen "large loop" battery cables a couple of times in solar
installs myself out on islands way down south. Also on boats/RV's/motor
homes.
Please keep the cable loop in mind when you do bench tests of inverters,
as it may screw up the results and make it seem like there is something
wrong with the inverter.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Xantrex Brand | CANADA |
Sales Application Engineer
Phone: +604-422-2528 | Tech Support: 800-670-0707 | Mobile:
+604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.Xantrex.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
<mime-attachment.gif>
<mime-attachment.gif>
<mime-attachment.gif>
<mime-attachment.gif>
<mime-attachment.gif>
*** Please consider the environment before printing this e-mail
From:
"boB at midnitesolar.com" <boB at midnitesolar.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>,
Date:
06/28/2015 10:30 PM
Subject:
Re: [RE-wrenches] Battery Bank to Inverter Wiring
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
On 6/28/2015 9:20 AM, Allan Sindelar wrote:
>>>>I'm not an EE, but I can't see what difference twisting would make in
the absence of a building/collapsing field as is normal with AC.<<<<
It is little known that with the typical inverters that use the heavy
power transformers,
have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed in
with that DC battery current.
The AC output current reflects back to the input as ripple current. This
is why you want to
have at least short as possible Sbattery cable runs AND keep the wires as
close together as possible.
Twisting the battery cables may help a bit but that is probably overkill.
The problem has to do with inductance in the battery cables. You can use
as big of cable
as you can fit in to reduce resistance, but that will not help to lower
the inductance.
The problems you can sometimes have with high inductance is that L-C
resonance at the
inverter can raise the peak voltages seen at the inverter input terminals
and can be hard on
the inverter.
Then again, the high frequency, lighter weight inverters will typically
keep most of that ripple
inside, between the DC input and AC output and battery cable inductance
will not be as much
of a problem on the battery cables.
boB Gudgel
On 6/28/2015 9:20 AM, Allan Sindelar wrote:
As a matter of course I have always run the positive and negative
conductors of high-current cable pairs together, but have never
deliberately twisted them, and have never known of any related problems.
The most obvious example of this would be 4/0 battery/inverter cables in a
24V system, with a 250A GJ-class breaker or (prior to that) a 300A or 400A
Class T fuse. It's pretty tough to thread a twisted pair of 4/0
USE/RHH/RHW cables through a 2" elbow or LB from inverter enclosure to
battery enclosure.
I'm not an EE, but I can't see what difference twisting would make in the
absence of a building/collapsing field as is normal with AC.
I have twisted AC conductors together in the past when clients have
expressed concerns about EMF from their equipment and wiring, but only AC.
Allan
Allan Sindelar
allan at sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell
On 6/27/2015 2:40 AM, John wrote:
That is why for years we have been twisting those leads around each
other. I was told it was to cancel out the opposing fields on the wires,
but for whatever the correct technical reason is, we have always twisted
those heavy wires. John V.
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Jarmo.Venalainen at schneider-electric.com
Sent: Saturday, 27 June 2015 5:45 a.m.
To: RE-wrenches
Subject: [RE-wrenches] Battery Bank to Inverter Wiring
Hi:
>From time to time over the years I've come across systems where the
routing of DC cables between the batteries and the inverter has been the
cause of issues.
I'm not referring to wire thickness or quality of terminations. For the
purposes of this discussion, just assume that wire thickness and
terminations are perfect.
What I am referring to is the routing of the positive and negative battery
cables. In particular, the loop area within the + and - cables as shown
in the image below,
The problem I've seen in systems with a large loop in the setup is that
the inverter does not provide good surge power and can even go into low
voltage shutdown during large surges.
Recently this happened again and I wanted to get a better feel for it, so
I did some math.
For a cable length of about 12', the loop is an inductor which has a value
of inductance of about 1 uH for side by side cables and as much as 6 uH
for cables about 1 foot apart.
This inductance is greatly multiplied by any ferrous metal in the loop and
can easily be in the range of 10's to 100's of uH. Examples being cables
which run in steel conduits or along the steel frame of a motor home.
Inductance causes a voltage drop proportional to the rate at which the
current is changing. To get an idea of how large that rate can be for
typical inverters, I did surge tests with a 5kW inverter and found that
the rate of change of current can be as high as 100A per milli-second or
100,000 Amps/second.
Given that, the voltage drop of the wire inductance is then , Vdrop =
(rate of change of current) x (inductance),
Vdrop for 1 uH = (100,000 A/s) x (0.000001 H) = 0.1V
Vdrop for 10 uH = (100,000 A/s) x (0.000001 H) = 1.0V
Vdrop for 100 uH = (100,000 A/s) x (0.000001 H) = 10.0V clearly this is
a problem.
Have any of the wrenches had systems with this issue? If so, how often.
JARMO
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/ca8cea57/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 139354 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/ca8cea57/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 40194 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/ca8cea57/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 4274 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/ca8cea57/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1869 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/ca8cea57/attachment-0003.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1897 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/ca8cea57/attachment-0004.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2041 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/ca8cea57/attachment-0005.gif>
More information about the RE-Wrenches
mailing list