[RE-wrenches] Battery Bank to Inverter Wiring

jerrysgarage01 jerrysgarage01 at gmail.com
Mon Jun 29 18:21:26 EDT 2015


Wrenches
We always try to minimize in connection cables as well as home run cables to the shorted length possible, restating batteries to aid this should always be considered as well as positive and negative runs
Jerry


Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone

<div>-------- Original message --------</div><div>From: Ray Walters <ray at solarray.com> </div><div>Date:06/29/2015  12:05 PM  (GMT-10:00) </div><div>To: RE-wrenches <re-wrenches at lists.re-wrenches.org> </div><div>Subject: Re: [RE-wrenches] Battery Bank to Inverter Wiring </div><div>
</div>This is fascinating because while I knew the DC cables had an AC  component, I never realized how much inductance played in the volt drop to the inverter.  Thanks for bringing this to our attention     Jarmo.  
Which brings up another question based on Benn's question:  isn't the battery itself part of the inductive loop?  and would the lead inside and steel cases act to increase the inductance?  Should we consider changing battery layouts not just to shorten cable lengths, but to counter inductance in the batteries themselves?  If needed, we could actually wire the batteries to "twist" by putting every other 2 v cell in the opposite row.  
My guess is that it wouldn't be worth it, but I've been wrong many times.......

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 6/29/2015 3:55 PM, Benn Kilburn wrote:
What about when you have the (+) and (-) terminals at opposite ends of a larger battery bank?  Sure you can run the conductors side-by-side once they meet up on their way to the inverter, but would you consider the distance between the end terminals a "large loop"? 
Ideally the battery string is laid out so the end terminals are close together and close to the inverter, but this isn't always the case. 

Benn Kilburn
SkyFire Energy Inc. 
780-906-7807


On Jun 29, 2015, at 10:28 AM, Jarmo.Venalainen at schneider-electric.com wrote:

Hi: 

From the comments so far, it appears             that within the wrenches group, good practices are the rule and DC cables are kept side by side, so the problem I mentioned hasn't come up much. 

I have seen "large loop" battery cables a couple of times in solar installs myself out on islands way down south.  Also on boats/RV's/motor homes. 

Please keep the cable loop in mind when you do bench tests of inverters, as it may screw up the results and make it seem like there is something wrong with the inverter.           

JARMO
_____________________________________________________________________________________ 

Jarmo Venalainen  |   Schneider Electric                 |  Xantrex               Brand  |   CANADA  |   Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support:             800-670-0707  |   Mobile: +604-505-0291 
Email: jarmo.venalainen at schneider-electric.com  |   Site: www.Xantrex.com  |   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
<mime-attachment.gif>
<mime-attachment.gif>                 	<mime-attachment.gif>                 	<mime-attachment.gif>                 	<mime-attachment.gif>


*** Please consider the environment before printing this e-mail



From:	"boB at midnitesolar.com"                     <boB at midnitesolar.com>                 
To:	RE-wrenches <re-wrenches at lists.re-wrenches.org>,
Date:	06/28/2015 10:30 PM
Subject:                 	Re: [RE-wrenches] Battery Bank to Inverter Wiring
Sent by:                 	"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>




On 6/28/2015 9:20 AM, Allan Sindelar wrote:
>>>>I'm not an EE, but I can't see what difference twisting would make in
the absence of a building/collapsing field as is normal with AC.<<<<

It is little known that with the typical inverters that use the heavy power transformers,
have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed in with that DC battery current.

The AC output current reflects back to the input as ripple current.  This is why you want to
have at least short as possible Sbattery cable runs AND keep the wires as close together as possible.

Twisting the battery cables may help a bit but that is probably overkill.

The problem has to do with inductance in the battery cables. You can use as big of cable
as you can fit in to reduce resistance, but that will not             help to lower the inductance.
The problems you can sometimes have with high inductance is             that L-C resonance at the
inverter can raise the peak voltages seen at the inverter input terminals and can be hard on
the inverter.

Then again,  the high frequency, lighter weight inverters will typically keep most of that ripple
inside,  between the DC input and AC output and battery cable inductance will not be as much
of a problem on the battery cables.

boB Gudgel




On 6/28/2015 9:20 AM, Allan Sindelar wrote: 
As a matter of course I have always run the             positive and negative conductors of high-current cable pairs together, but have never deliberately twisted them, and have never known of any related problems. 
The most obvious example of this would be 4/0             battery/inverter cables in a 24V system, with a 250A GJ-class breaker or (prior to that) a 300A or 400A Class T fuse. It's pretty tough to thread a twisted pair of 4/0 USE/RHH/RHW cables through a 2" elbow or LB from inverter enclosure to battery enclosure.
I'm not an EE, but I can't see what difference twisting would make in the absence of a building/collapsing field as is normal with AC. 
I have twisted AC conductors together in the past when clients have expressed concerns about EMF from their equipment and wiring, but only AC.
Allan
Allan Sindelar
allan at sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

 

On 6/27/2015 2:40 AM, John wrote: 
That is why for years we have               been twisting               those leads around each other.  I was told it was to               cancel out the opposing fields on the wires, but for whatever the correct technical reason               is,  we have always twisted those heavy wires.                       John V.             
  
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jarmo.Venalainen at schneider-electric.com
Sent: Saturday, 27 June 2015 5:45 a.m.
To: RE-wrenches
Subject: [RE-wrenches] Battery Bank to Inverter Wiring 
  
Hi: 

From time to time over the years I've come across systems where the routing of DC cables between the batteries and the inverter has been the cause of  issues. 

I'm not referring to wire thickness or quality of terminations.  For the purposes of this discussion, just assume that wire               thickness and terminations are perfect.               

What I am referring to is the routing of the positive and negative battery cables.  In particular, the loop area within the + and - cables as shown in the image below, 

The problem I've seen in systems with a large loop in the setup is that the inverter does not provide good surge power and can               even go into low               voltage shutdown during large surges. 

Recently this happened again and I wanted to get a better feel for it, so I did some math.   

For a cable length of about 12', the loop is an inductor which has a value of inductance of about 1 uH for side by side cables and as much as 6 uH for cables about 1 foot apart.   

This inductance is greatly multiplied by any ferrous metal in the loop               and can easily be in the range of 10's to 100's of uH.  Examples being cables which run in steel conduits or along the steel               frame of a motor               home. 

Inductance causes a voltage drop proportional to the rate at which the current is changing.  To get an idea of how large that rate can be for typical inverters, I did surge tests with a 5kW inverter and found that the rate of change of current can be as high as 100A               per milli-second or 100,000 Amps/second. 

Given that, the voltage drop of the wire inductance is then , Vdrop = (rate of change of current) x (inductance), 

Vdrop for 1 uH = (100,000 A/s) x (0.000001 H) = 0.1V 
Vdrop for 10 uH = (100,000 A/s) x (0.000001 H) = 1.0V 
Vdrop for 100 uH = (100,000 A/s) x (0.000001 H) = 10.0V    clearly this is a problem. 

Have any of the wrenches had systems with this issue?  If so, how often. 


JARMO




______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
_____________________________________________________________________________________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150629/26f02fd1/attachment.htm>


More information about the RE-Wrenches mailing list