Hi:
>From time to time over the years I've come across systems where the
routing of DC cables between the batteries and the inverter has been the
cause of issues.
I'm not referring to wire thickness or quality of terminations. For the
purposes of this discussion, just assume that wire thickness and
terminations are perfect.
What I am referring to is the routing of the positive and negative battery
cables. In particular, the loop area within the + and - cables as shown
in the image below,
The problem I've seen in systems with a large loop in the setup is that
the inverter does not provide good surge power and can even go into low
voltage shutdown during large surges.
Recently this happened again and I wanted to get a better feel for it, so
I did some math.
For a cable length of about 12', the loop is an inductor which has a value
of inductance of about 1 uH for side by side cables and as much as 6 uH
for cables about 1 foot apart.
This inductance is greatly multiplied by any ferrous metal in the loop and
can easily be in the range of 10's to 100's of uH. Examples being cables
which run in steel conduits or along the steel frame of a motor home.
Inductance causes a voltage drop proportional to the rate at which the
current is changing. To get an idea of how large that rate can be for
typical inverters, I did surge tests with a 5kW inverter and found that
the rate of change of current can be as high as 100A per milli-second or
100,000 Amps/second.
Given that, the voltage drop of the wire inductance is then , Vdrop =
(rate of change of current) x (inductance),
Vdrop for 1 uH = (100,000 A/s) x (0.000001 H) = 0.1V
Vdrop for 10 uH = (100,000 A/s) x (0.000001 H) = 1.0V
Vdrop for 100 uH = (100,000 A/s) x (0.000001 H) = 10.0V clearly this is
a problem.
Have any of the wrenches had systems with this issue? If so, how often.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Xantrex Brand | CANADA |
Sales Application Engineer
Phone: +604-422-2528 | Tech Support: 800-670-0707 | Mobile:
+604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.Xantrex.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150626/007d6cce/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14647 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150626/007d6cce/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 40194 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150626/007d6cce/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 4274 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150626/007d6cce/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1869 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150626/007d6cce/attachment-0003.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1897 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150626/007d6cce/attachment-0004.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2041 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150626/007d6cce/attachment-0005.gif>
More information about the RE-Wrenches
mailing list