[RE-wrenches] Voltage Degradation with Uni-Solar laminate
Rebekah Hren
rebekah.hren at gmail.com
Mon Jun 1 13:24:05 EDT 2015
Attached is a screenshot of an example calculation from SEI for minimum
modules in series for controllers, similar to Jarmo's but more
system-specific. And fairly conservative because of the 1.2 factor for
degradation over time (which includes voltage drop). Note there are values
specific to the site, batteries, and module - this example was for a roof
mounted array thus the 30ºC cell temp adder.
SEI recommends not going lower than 1.1 times bulk voltage for the target
minimum array voltage although 1.2 is a good target to start with.
One thing I'd note is that for systems without a generator or other
charging source besides PV the target array voltage should be 1.2
times *equalize
voltage* not bulk voltage. And of course a maximum modules in series calc
has to be done too.
[image: Inline image 1].
Cheers,
Rebekah