[RE-wrenches] ConnectDER

Dave Click daveclick at fsec.ucf.edu
Tue May 26 11:10:55 EDT 2015


I have had two of these on my house (I upgraded my system, so had to get 
a larger model) and I really like them. Great guys at the company and 
great product. Major issue is that most utilities don't have a blanket 
allowance for meter collars like this one, so you may end up spending a 
fair amount of time trying to get a utility's approval without guarantee 
of success. For utilities who think that customer-owned PV is The Devil, 
it could be a tough sell trying to get them to make your job easier. 
This can be a lifesaver on some projects where strict 690.64 compliance 
can be expensive-- encountering a 60A interconnection on a 150A service 
makes this worth fighting for, especially on all-in-ones or older 
equipment that the homeowner isn't ready to replace.

Dave



On 2015/5/25 19:58, toddcory at finestplanet.com wrote:
>
> wow, engenius. thanks for posting this.
>
> http://connectder.com/products
>
> todd
>
>
>
> On Monday, May 25, 2015 4:48pm, "John Blittersdorf" 
> <john.blittersdorf at gmail.com> said:
>
> Bill,
>    One clean way to do it would be to use a ConnectDER, but the max 
> input is 11.5 kw.  We have used several of these for under 10 k 
> installations and have saved lots of install time.   They are not 
> cheap (approx $300+).  Our power company sells them to installers.
> John Blittersdorf
> Central Vermont Solar & Wind
>
> On Mon, May 25, 2015 at 12:39 AM, frenergy <frenergy at psln.com 
> <mailto:frenergy at psln.com>> wrote:
>
>     Wrenches,
>             Customer currently has a hacked up 200 amp Sylvania
>     meter/mains panel.  He also is averaging a load of 74 KWhrs/day!
>     which will require about 15  KW system size at this site. 
>     Obviously a system this size cannot backfeed the busses in the
>     load center.  Because the exiting panel is a mess anyway, I'm
>     suggesting it gets changed out.
>             What sort of new 200 amp service would facilitate a clean
>     supply side connection.  One thought is have separate Utility
>     meter socket then a 12 X 12 J-box with a monster power
>     distribution block in it and then a distribution panel (without
>     the meter socket)...this being a way to insert a means to grid-tie
>     between the meter and the 200 amp main breaker.  A little spendy
>     but nothing like going to higher amp service to be able to load
>     side connect.
>             A 400 amp panel is not an option as the existing 165' of
>     3" pvc underground conduit to the pole currently has 4/0 alum. 
>     The utility says it would have to be 4" for the new cable and the
>     cost $10K+ for the upgrade.
>             Other ideas??
>     Thanks in advance
>     Bill
>     Feather River Solar Electric
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> Sent from Finest Planet WebMail.
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150526/0d1199a4/attachment.htm>


More information about the RE-Wrenches mailing list