[RE-wrenches] FLA battery set points with larger arrays
Jason Szumlanski
jason at floridasolardesigngroup.com
Mon May 25 15:49:50 EDT 2015
Steve,
Can you elaborate on how heat affects batteries that sit in float service
at high temperatures? What kind of cycle/capacity changes can we expect?
Say, for example, that a bank of S-530 batteries are 5 years old and have
spent days at 40C and nights at 25C, and have essentially been in float
service except for a couple dozen cycles to 50% over the years. If these
batteries are now put into regular daily cycles at the same temperatures,
would they act much differently than batteries that were stored at a
constant 25C?
I guess my question boils down to whether cycling during high temperatures
is more damaging than just being "stored" at high temperatures.
Thanks,
Jason
On Mon, May 25, 2015 at 1:14 PM, Steve Higgins <steve at surrette.com> wrote:
> Typically you want the BTS installed and any and every case… The BTS
> should be installed below the level of the plates not on the top of the
> battery. To do this you need to have the BTS about 1/3 to ½ the way down
> the side (Single Wall) of the battery, and I would suggest running some
> duct tape around the battery on the sensor to keep it on the side of the
> battery.
>
>
>
> For a Double wall battery, Although the sensor will be close, it will get
> better readings in between the plastic walls. To do so you can pull the
> top off the battery and put it between the walls. There is usually some
> black silicone around the pos/neg terminals, all you need to do is replace
> that with regular old RTV silicone…
>
>
>
> Post mounts are okay, but Surrette prefers the side mounts with another
> method of securing the sensors… The post mounts only sense the plate temp,
> not the overall temp of the battery.
>
>
>
> Temperature is a killer, and my years at Outback, and Trace I had no idea
> of how damaging this was until I came to work for Surrette.
>
> For every 10 Degrees C above 25 you lose 50% of your life cycles… For
> example if you installed these in the Mojave desert where six month of the
> year they would reach 95F+ you would probably lose about 25-30% of your
> life cycles… One of the ways to combat this if you can is vault them…it’s a
> lot of work, but the earth even in those environments will keep them
> cooler.
>
>
>
>
>
>
>
>
>
>
>
>
>
> *Steve Higgins Technical Services Manager *P: +1.902.597.4020
> M: +1.206.790.5840
> F: +1.902.597.8447
>
> *Surrette Battery Company *Exclusive manufacturer of
> <http://www.rollsbattery.com>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Ray Walters
> *Sent:* Saturday, May 23, 2015 8:05 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] FLA battery setpoints with larger arrays
>
>
>
> Having the LVD be temperature compensated so that the load is always
> disconnected above the freeze point of the battery would be a Huge
> Improvement on the whole concept of LVD. In combination with State of
> Charge monitoring, like the Whiz bang Jr, would be the most effective, and
> just program the disconnect to stay above freezing for a typical lead acid
> battery. I got this from a Trojan White Paper:
>
>
> R.Ray Walters
>
> CTO, Solarray, Inc
>
> Nabcep Certified PV Installer,
>
> Licensed Master Electrician
>
> Solar Design Engineer
>
> 303 505-8760
>
>
>
>
> FLA batteries will freeze easier if they are discharged. I suppose that
> you could
> use the battery temp sensor to make sure you charge them up good when
> the temp gets cold enough.
>
> boB
>
> This email and its attachments have been scanned by mailWatch E-Mail
> Firewall for viruses, spam, and malicious content. The information
> transmitted in this email is intended only for the entity or person to
> which it is addressed and may contain confidential/privileged material. If
> you received this in error, please contact the sender and delete the
> material from any computer. Any review, retransmission, dissemination, or
> other use of this information by persons or entities other than the
> intended recipient is strictly prohibited
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150525/db13bafb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 42122 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150525/db13bafb/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: rollsafb380
Type: image/jpeg
Size: 11941 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150525/db13bafb/attachment.jpe>
More information about the RE-Wrenches
mailing list