[RE-wrenches] FLA battery setpoints with larger arrays
boB at midnitesolar.com
boB at midnitesolar.com
Sat May 23 02:44:43 EDT 2015
On 5/22/2015 6:43 PM, jay peltz wrote:
> agreed.
> Again, maybe Steve has an view of the builder, but having it on the
> post is pretty close.
If it's the typical flat type of BTS, wedged right between two batteries
will give a good
average temperature of the two of them.
boB
>
>
> Maybe there is a white paper on temp sensor locations pros/cons?
>
> jay
>
>
>
>
> On Fri, May 22, 2015 at 5:08 PM, frenergy <frenergy at psln.com
> <mailto:frenergy at psln.com>> wrote:
>
> This is good stuff, enlightening...but begs another small? detail
> that has obvious big ramifications. Where o where does the BTS get
> placed to best read the actual "temperature of the battery"? It's
> too big to fit on many terminals especially once cabled, it's
> certainly not very accurate when stuck to the outer case of a dual
> cased Surrette and probably only somewhat more accurate when stuck
> to an L-16 top. Aren't we looking for electrolyte temps?
> Many times the BTS doesn't survive its original location
> after a few years of battery acid. Rather than "insulated" from
> the surface its been assigned to with 2-sided tape, it seems like
> it should be in direct contact with that surface with a dab of
> thermal grease between. Or, couldn't a wrench be trusted to drill
> a 1/4" hole in the top of a representative cell and insert an acid
> proof sensor into the electrolyte with a formed snap-in plug
> (rubber, silicone, nylon??) behind it on the lead, to seal it
> where it enters the battery case?
> Just saying, if we really need (and I think we do)
> accurate battery temp for temp regulation and battery health, what
> we're using now is substandard.
> Bill
> Feather River Solar Electric
>
> ----- Original Message -----
> *From:* Ray Walters <mailto:ray at solarray.com>
> *To:* RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
> *Sent:* Friday, May 22, 2015 3:33 PM
> *Subject:* Re: [RE-wrenches] FLA battery setpoints with larger
> arrays
>
> I thought I'd post some info on Battery Temp from a few manus:
> HUP Solar One: do not exceed 105 F
> Full River AGMs: max recommended operating temp 104F
> and from Trojan: for every 10C increase in temperature the
> reaction rate doubles. Thus, a month of operation at 35C is
> equivalent to 2 months at 25C. Heat is the enemy of ALL lead
> acid batteries. Even small increases in temperature will have
> a major influence on battery life.
> Their T105 RE battery has a max operating temperature of 113 F
>
> I think more batteries are hitting high temperatures than we
> may realize. This info from Trojan that a battery at 95F
> (35C) will only last half its rated life (at 25C) is very
> concerning.
> Once again, thanks Bob and Midnite for giving us a tool to
> combat over temperature of batteries. We always knew cold was
> a problem, now I'm realizing heat could be just as important.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar De
>
> --
> Jay Peltz
> Peltz Power
> jay.peltz at gmail.com <mailto:jay.peltz at gmail.com>
>
>
-------------- next part --------------