[RE-wrenches] Load testing Lithium battery bank
Larry
larry at starlightsolar.com
Tue Mar 17 15:40:35 EDT 2015
Hey Ray,
I remember seeing huge banks of light bulbs as loads back in the early
70's.
I need to test the entire bank as one unit as the first cell of 32 to
reach 2.8 volts determines the capacity for the bank. I just saw Home
Depot has a 2kW 120 volt water heater for $10. Guess I need to do some
welding.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
On 3/17/15 11:59 AM, Ray Walters wrote:
> Hi Larry,
>
> I think you hit on the best load already: water heater elements rated
> for 120 v. We have also used dump loads for wind turbines like the
> air heating elements from Bergey, but they are only about 1 kW each.
> Another possible source are the resistor banks for old golf carts
> (before they had controllers, they used resistor banks to operate at
> slow speeds)
> A very long time ago, an inverter company had a demonstration that
> used a large bank of incandescent light bulbs. They used to make a
> 300 watt bulb for mining, so 33 of those would work. (maybe a few
> more bulbs, since your voltage is bit lower than 120 v) Cheap
> electric space heaters would work too. You also might look around at
> an electronics surplus store.
> Whatever you do, it sounds like a lot of time and work to set up. Any
> chance of doing a smaller load test for subsets of the total bank?
> You might be able to use a standard 12 v battery load tester then.
>
> Good Luck.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> On 3/17/2015 12:41 PM, Larry wrote:
>> I am repairing and restoring a pair of poorly designed lithium-ion
>> battery bank that suffered over discharge, damaging many cells. After
>> cell replacement I need to perform a discharge test with a 10kW load
>> to verify the remaining capacity. The battery voltage is 105 volts @
>> 100% SoC and 89.6 volts @ 0%
>>
>> I would like advice on how I can create an economical 10kW load.
>> Water heating element? Wire wound resistors? Are there any GT
>> inverters that will operate at these voltages?
>>
>> Thanks.
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
More information about the RE-Wrenches