[RE-wrenches] Outback quad stack X240 breaker tripping
Chris Worcester
chris at solarwindworks.com
Wed Mar 11 17:59:30 EDT 2015
Hi Kevin,
I have seen the X240's trip off like this when theyare over loaded. When this was happening to us the slave inverters had blown AC boards and some times Control and FET boards too. We had a hard time diagnosing this as their green lights were on. Using a clamp on amp meter on each inverter's AC IN conductor while charging with the gen set allowed us to compare their charging currents to each other. Typically the ones with blown AC boards output would be close to zero amps. So the X240's were doing double duty and they will smoke too if the inverters aren't delta with.
Sincerely,
Chris Worcester
530-448-9692
Sent from my Galaxy S®III
<div>-------- Original message --------</div><div>From: Kevin Pegg <kpegg at energyalternatives.ca> </div><div>Date:03/11/2015 1:19 PM (GMT-08:00) </div><div>To: RE-wrenches <re-wrenches at lists.re-wrenches.org> </div><div>Subject: [RE-wrenches] Outback quad stack X240 breaker tripping </div><div>
</div>Hello Wrenches,
Customer in remote location has a strange situation come up on an existing system installed (by others) 6 or so years go. Quad stack VFX3648.
Last night gen start was triggered by low voltage - a normal system operation.
Approx 1h into charge, they lost 1/2 the circuits in house - L2 de-energized. Caretaker went to check power system and noticed the X240 breakers tripped. Tried to reset but it tripped out right away. So he left it as is and called me in the morning.
Here's what I've been able to determine today:
- The x240 is installed to bridge L1 & L2 on the load side.
- with master inverter on, 3 slaves off, both L1 and L2 energized so suggests x240 is working.
- within 10 seconds of generator on and charging, x240 breaker trips (and makes L2 go dark).
- loads are minor, ~1,000 w of misc lights and such, isn't all loaded up on one leg.
Appreciate any thoughts to remedy. I'm not as familiar with this config as others.
Kevin Pegg
EA Energy Alternatives Ltd.
37471 Hwy 16 E
Telkwa, BC V0J 2X2
250-846-9888
Http://www.EnergyAlternatives.ca
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150311/641d460c/attachment.htm>
More information about the RE-Wrenches
mailing list