[RE-wrenches] Main Service Fuse rated higher than Bus Rating of attached sections?
Mark Frye
markf at berkeleysolar.com
Tue Feb 17 11:37:00 EST 2015
1. You need to know the actual rating of any sub-section buss that you
will be backfeeding with PV. Do not backfeed this buss with more than
100% of it's ampacity.
2. Evaluate 120% of the 4000A buss against the 3500A main and all PV
backfeed all of the subsections.
Mark Frye
On 2/17/2015 7:37 AM, Allen Frishman wrote:
> Mark,
> Thank you, your response is very helpful! How does the 120% rule
> get applied to the 1000A sections in my example? When grid connecting
> downstream on the load side of the switches on the 1000A sections do
> we ignore the rating of the 1000A bus bar being protected by a 3500
> Amp Fuse? If yes what section in the code allows this?
>
>
> /Al Frishman/
> AeonSolar
>
> /(917) 699-6641 <tel:%28917%29%20699-6641> - cell/
> /(888) 460-2867 <tel:%28888%29%20460-2867>/
> /www.aeonsolar.com <http://www.aeonsolar.com/>/
>
>
> On Feb 17, 2015, at 10:23 AM, Mark Frye wrote:
>
>> NEC 2008, 240.21 (B)(1)(1) a.
>>
>> Each of the smaller buss sections are feeders which are sized
>> according to the tap rules. I believe the answer to your question is
>> that the larger fuse can't protect the smaller buss. *But*, the
>> likelihood of a short developing in that section of the circuit is
>> very small and if one did, damage to the equipment would be limited
>> that area. This is the essence of allowing taps.
>>
>> Mark Frye
>>
>> On 2/17/2015 6:17 AM, Allen Frishman wrote:Wrenchers,
>>> I run into lots of Service Equipment that has a Large Service Switch
>>> which feeds multiple Sections with the Bus bar on each section rated
>>> significantly less than the main bus. A specific example that I
>>> am currently looking at has a 4000Amp Switch with a 3500 Amp Fuse
>>> which feeds 3 (1000 Amp) switchgear sections. How is it possible
>>> that the 3500 Amp Fuse protects the (3) 1000 Amp Sections? In
>>> this particular case each of the 1000 Amp Sections has between 3 and
>>> 6 fused switches on them. The sum of those switch/fuse ratings
>>> exceeds 1000 Amps in each case. For reference - This service gear
>>> is over 40 years old.
>>>
>>> All thoughts are appreciated.
>>>
>>> /Al Frishman/
>>> AeonSolar
>>>
>>> /(917) 699-6641 <tel:%28917%29%20699-6641> - cell/
>>> /(888) 460-2867 <tel:%28888%29%20460-2867>/
>>> /www.aeonsolar.com <http://www.aeonsolar.com/>/
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150217/f8f70ec3/attachment.htm>
More information about the RE-Wrenches
mailing list