[RE-wrenches] Outback AGS & eq
William Miller
william at millersolar.com
Thu Feb 12 18:27:05 EST 2015
Mac:
Apparently so, but this operation is not supported. It supposedly works.
William
> On Feb 12, 2015, at 3:18 PM, Mac Lewis <maclewis1 at gmail.com> wrote:
>
> Hi Jay & William,
>
> Just so I understand, you can put the mate into auto right after the eq is enabled (not after eq has finished), and it will manage the generator? Is that right?
>
> Thanks
>
>> On Thu, Feb 12, 2015 at 10:45 AM, jay peltz <jay at asis.com> wrote:
>> I"ve had clients do it for years with no problems that I know of.
>>
>> jay
>>
>> peltz power
>>
>>
>>
>>> On Feb 12, 2015, at 9:47 AM, <william at millersolar.com> wrote:
>>>
>>> Friends:
>>>
>>> I understood the generator had to be started and stopped manually. I have a client who was using the sequence below to stop the generator automatically. To have the generator stop automatically has a convenience factor, but I do like my clients to verify the cycle has accomplished the prescribed regimen, and walking away from the process does not accomplish that.
>>>
>>> I spoke with Outback regarding the procedure of engaging the auto mode prior to completion of the EQ and the reply was that the system had not been engineered to operate this way so the results could not be guaranteed.
>>>
>>>
>>> William
>>>
>>> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
>>> Sent: Thursday, February 12, 2015 8:54 AM
>>> To: RE-wrenches
>>> Subject: Re: [RE-wrenches] Outback AGS & eq
>>>
>>> Hi Mac
>>>
>>> I don't think there is a global eq function.
>>> Eq continues to be manual on inverters.
>>>
>>> Gen to manual on
>>> Initiate EQ
>>> Gen to auto
>>> Done
>>>
>>>
>>> Jay
>>> Peltz power.
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>
>
>
> --
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." -Sócrates
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150212/b42ef069/attachment.htm>
More information about the RE-Wrenches
mailing list