The inverters' input capacitors may be charged and so that must also be
isolated near the inverter.
A grid operated contactor will not work for a battery-back up system.
Also, 600V DC can weld contacts closed and if this happens and there is
no feedback to show that
the contacts definitely opened, this can ruin a firefighter's day.
Otherwise, a system of contactors from AC grid could work in a grid-tie
only system.
The new UL rapid shutdown specifications are supposed to be released
very soon now.
Maybe within the month ?
boB Gudgel
K7IQ
MidNite Solar
On 2/2/2015 1:23 PM, Mark Frye wrote:
> In order to clear up the conversation...
>
> I you put a relay in a box within 10 feet of the array on the roof,
> you can use an relay with a DC rated Normally Open contact to open and
> connect/isolate the array DC voltage.
>
> You can drive the coil of that relay with either AC or DC, but either
> way, if you lose voltage to drive the coil, the contact opens and
> isolates.
>
> My point is, for simple grid-tied system, there is no need for a
> "stop" switch anywhere in the system. It doesn't matter whether the
> contactor coil is driven by the premise AC or by a DC power supply
> connected to the premise AC, when the the main is opened or the meter
> pulled, the array Dc will become isolate.
>
> Therefore, there is no need for the "stop" switch and yet as I
> understand it, such a switch is now required by the Code. The switch
> is not needed but is required.
>