I see. So they have another box on the ground floor with the "kill" 
switch and that box includes a 120/240 vac to 24vdc xfrm to drive the 
contactor coil  on the roof? So you run 120/240 vac to the box with the 
"kill" switch?

Mark Frye
On 2/2/2015 10:52 AM, Glenn Burt wrote:
>
> Looks like they use 24VDC for contactor activation, not 120VAC.
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] 
> *On Behalf Of *Mark Frye
> *Sent:* Monday, February 02, 2015 1:29 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Rapid Shut Down and the 10 Second Rule 
> Questions
>
> OK. So did you run a line 120V up to the box on the roof to energize 
> the coil of the relay up there?
>
> Mark Frye
>
> On 2/2/2015 9:13 AM, Jerry Shafer wrote:
>
>     The units we have used have a large contactor inside the combiner
>     box made by AMtec Solar. this was required to control the shut
>     down includes a fire button done on the ground floor
>
>     Jerry
>
>     On Mon, Feb 2, 2015 at 5:49 AM, Mark Frye <markf at berkeleysolar.com
>     <mailto:markf at berkeleysolar.com>> wrote:
>
>     Jerry,
>
>     What unit did you use?
>
>     Mark Frye
>
>     On 2/2/2015 7:43 AM, Jerry Shafer wrote:
>
>         Wrenches
>         We have installed some of these rapid shut down units and they
>         are always located close to the array and ours kill the DC
>         instantly as long as the inverter was running when this
>         accures did not test it with inverters already off.
>         Jerry
>
>         On Feb 2, 2015 5:34 AM, "Christopher Warfel"
>         <cwarfel at entech-engineering.com
>         <mailto:cwarfel at entech-engineering.com>> wrote:
>
>         We have a interpretation problem among some people I work with
>         with, and  690.12 Rapid Shut Down and the the 10 second time
>         for reducing ac and dc conductors to 240ma, and 30V.  The word
>         "initiation" seems to indicate that all affected conductors
>         need to be at these levels within 10 seconds of de-energizing
>         either the ac or dc conductors. If so, then the disconnects
>         need to be co-located to meet this requirement if this
>         interpretation is correct.
>
>         I have read Mr. Brook's article in Solar Pro, but AHJs may
>         feel differently.
>
>         Would anyone care to weigh in on their interpretation?
>
>         Thank you, Chris
>
>
>
>
>
>         -- 
>         Christopher Warfel, President
>         ENTECH Engineering, Inc.
>         PO Box 871, Block Island, RI 02807
>         401-466-8978 <tel:401-466-8978>
>
>
>         _______________________________________________
>         List sponsored by Redwood Alliance
>
>         List Address: RE-wrenches at lists.re-wrenches.org
>         <mailto:RE-wrenches at lists.re-wrenches.org>
>
>         Change listserver email address & settings:
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>         List-Archive:
>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>         List rules & etiquette:
>         www.re-wrenches.org/etiquette.htm
>         <http://www.re-wrenches.org/etiquette.htm>
>
>         Check out or update participant bios:
>         www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>         _______________________________________________
>
>         List sponsored by Redwood Alliance
>
>           
>
>         List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>
>           
>
>         Change listserver email address & settings:
>
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>           
>
>         List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>           
>
>         List rules & etiquette:
>
>         www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>
>           
>
>         Check out or update participant bios:
>
>         www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>
>           
>
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>     _______________________________________________
>
>     List sponsored by Redwood Alliance
>
>       
>
>     List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>
>       
>
>     Change listserver email address & settings:
>
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>       
>
>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>       
>
>     List rules & etiquette:
>
>     www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>
>       
>
>     Check out or update participant bios:
>
>     www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>
>       
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150202/d556827d/attachment.htm>


More information about the RE-Wrenches mailing list