OK. So did you run a line 120V up to the box on the roof to energize the
coil of the relay up there?
Mark Frye
On 2/2/2015 9:13 AM, Jerry Shafer wrote:
> The units we have used have a large contactor inside the combiner box
> made by AMtec Solar. this was required to control the shut down
> includes a fire button done on the ground floor
> Jerry
>
> On Mon, Feb 2, 2015 at 5:49 AM, Mark Frye <markf at berkeleysolar.com
> <mailto:markf at berkeleysolar.com>> wrote:
>
> Jerry,
>
> What unit did you use?
>
> Mark Frye
>
>
> On 2/2/2015 7:43 AM, Jerry Shafer wrote:
>>
>> Wrenches
>> We have installed some of these rapid shut down units and they
>> are always located close to the array and ours kill the DC
>> instantly as long as the inverter was running when this accures
>> did not test it with inverters already off.
>> Jerry
>>
>> On Feb 2, 2015 5:34 AM, "Christopher Warfel"
>> <cwarfel at entech-engineering.com
>> <mailto:cwarfel at entech-engineering.com>> wrote:
>>
>> We have a interpretation problem among some people I work
>> with with, and 690.12 Rapid Shut Down and the the 10 second
>> time for reducing ac and dc conductors to 240ma, and 30V.
>> The word "initiation" seems to indicate that all affected
>> conductors need to be at these levels within 10 seconds of
>> de-energizing either the ac or dc conductors. If so, then the
>> disconnects need to be co-located to meet this requirement if
>> this interpretation is correct.
>>
>> I have read Mr. Brook's article in Solar Pro, but AHJs may
>> feel differently.
>>
>> Would anyone care to weigh in on their interpretation?
>>
>> Thank you, Chris
>>
>>
>>
>>
>>
>> --
>> Christopher Warfel, President
>> ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>> 401-466-8978 <tel:401-466-8978>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150202/93550104/attachment.htm>
More information about the RE-Wrenches
mailing list