[RE-wrenches] Rapid Shut Down and the 10 Second Rule Questions
Mark Frye
markf at berkeleysolar.com
Mon Feb 2 10:49:28 EST 2015
Jerry,
What unit did you use?
Mark Frye
On 2/2/2015 7:43 AM, Jerry Shafer wrote:
>
> Wrenches
> We have installed some of these rapid shut down units and they are
> always located close to the array and ours kill the DC instantly as
> long as the inverter was running when this accures did not test it
> with inverters already off.
> Jerry
>
> On Feb 2, 2015 5:34 AM, "Christopher Warfel"
> <cwarfel at entech-engineering.com
> <mailto:cwarfel at entech-engineering.com>> wrote:
>
> We have a interpretation problem among some people I work with
> with, and 690.12 Rapid Shut Down and the the 10 second time for
> reducing ac and dc conductors to 240ma, and 30V. The word
> "initiation" seems to indicate that all affected conductors need
> to be at these levels within 10 seconds of de-energizing either
> the ac or dc conductors. If so, then the disconnects need to be
> co-located to meet this requirement if this interpretation is correct.
>
> I have read Mr. Brook's article in Solar Pro, but AHJs may feel
> differently.
>
> Would anyone care to weigh in on their interpretation?
>
> Thank you, Chris
>
>
>
>
>
> --
> Christopher Warfel, President
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978 <tel:401-466-8978>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150202/50d24b5a/attachment.htm>
More information about the RE-Wrenches
mailing list