I believe that that breaker is primarily used for the charging circuit of the SWs.I usually find this tripped during the charge cycle. I would verify; when the breaker trips, check the charge settings menu10 + the AC2 input settings, also check that you don't have a bad battery causing over charging. Let me know off list as I have in my truck a 30A breaker that I use as a replacement for the SWs.Tump
On Jan 21, 2015, at 10:02 PM, Allan Sindelar wrote:

> Two relevant details of note here:
> 1. The breaker on only the 5548 model was of a "toggle switch" configuration, rather than the push button used on the rest of the models. If you have a push button as you describe, the problem may be that it was an incorrect previous replacement.
> 2. As Ray has noted, the 4048 could out surge the 5548. They had different firmware, giving the 5548 a tighter voltage window during surges, resulting in less surge capacity due to less tolerance for voltage dips under surge loads.
> Allan
> 
> Allan Sindelar
> allan at sindelarsolar.com
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>  
> On 1/21/2015 7:38 PM, Ray Walters wrote:
>> Try Mouser electronics.  Otherwise, I'd consider bypassing it, and have a regular breaker (30 or 40 amp) on theout put. 
>> The tripping was probably because the breaker was malfunctioning. Usually the SWs will trip their on board computer to shutdown for over current, and the breaker should never be used. The 5548s were kind of weird though.  I never liked those.  I've had SW4048s out surge the 5548s hands down.
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer, 
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>> On 1/21/2015 12:24 PM, don at energysolarnow.com wrote:
>>> Hi all- 
>>> I'm having some difficulty finding a replacement for the little push-button circuit breaker on an old Trace SW5548 inverter. This is located on the lower left corner of the box, below the wiring access panel. The customer has had             repeated tripping of this breaker from overcurrent, so it has been doing it's job. But now the button won't reset.
>>> It's a 35 amp breaker.  I have only been able to find smaller ones in the online catalogs.
>>> Anyone know of a better parts supplier?
>>> Thanks
>>> Don Barch
>>> Energy Solar
>>> 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> Tump at swnl.net               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                              
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20150122/84fac6a1/attachment.htm>


More information about the RE-Wrenches mailing list