[RE-wrenches] Magnum System - Discharged Battery Bank
Drake
drake.chamberlin at redwoodalliance.org
Thu Dec 18 10:59:38 EST 2014
One issue I see is that a 4.4 kW inverter is
being fed 7 kW. I don't know if this would
account for all you are seeing. Could the Magnum
could be shutting down on overcurrent?
At 09:27 PM 12/16/2014, you wrote:
>Wrenches,
>
>I visited a customer today whose grid-tied
>battery backup system suffered some sort ofÂ
>catastrophic failure, and now I'm trying to play
>detective to figure out what happened and whose equipment/design is to blame.
>
>Here is what I know so far:
>- System is ac-coupled with a Sunny Boy 7000
>(7.85kW array), Magnum MS4448PAE (x2), 3 strings of 4 12v batts (705Ah total)
>- Site visit was triggered by the Sunny Boy
>registering zero output via online monitoring.
>- SPST Solid state relay installed on Sunny Boy
>output, controlled via Magnum router, serves as
>secondary overcharge protection to Magnum's
>frequency shift feature. Technician who
>initially responded claims he measured 240v
>across the relay's terminals - relay
>manufacturer claims this is "100% impossible".
>We removed the relay from the circuit, and the Sunny Boy is again operational.
>- On arrival I found the Magnum display showing
>a "Low Battery Charge" message with the bank
>measuring ~4Vdc. The individual batteries were
>in various states of charge, ranging from high
>of 6.3v to low of -2.6v. These measurements were
>taken at rest, all battery cables disconnected,
>and yes three of the batts were registering a negative voltage.
>- Customer reports that he was not aware of any
>recent prolonged power outages.
>
>The three potential suspects would seem to be:
>- SS relay: The customer is convinced that this
>is the weak link in the system and somehow
>triggered this failure. I am not so convinced
>but would be interested to hear recommendations
>for properly testing its functionality.
>- Magnum equipment: Since there is
>low-battery-cutout protection, why would this
>feature not have activated and prevented the batteries from draining so low?
>- Batteries: I am not very familiar with modes
>of failure, but our distributor suggested that
>an internal short could be a possibility - what might have triggered this?
>
>Clearly I am fishing for potential leads here, so any suggestions are welcome.
>
>Thanks!
>--
>Corey Shalanski
>Joule Energy
>New Orleans, LA
>[]
>á§
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141218/11395cbd/attachment.htm>
More information about the RE-Wrenches
mailing list