[RE-wrenches] Programmable Battery Charger
Kirk Herander
kirk at vtsolar.com
Tue Dec 16 15:57:56 EST 2014
Thanks for the observation. I forgot it will rectify to the peak voltage.
Kirk Herander
VT Solar, LLC
Proven PV provider since 1991
<x-msg://519/www.vermontsolarnow.com> www.vermontsolarnow.com
dba Vermont Solar Engineering
NABCEPTM Inaugural Certificant
VT RE Incentive Program Partner
802.863.1202
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of jay peltz
Sent: Monday, December 15, 2014 8:51 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Programmable Battery Charger
Hi Kirk,
If you use a 200vdc midnight CC you'll have no issues.
When you rectify 120vac its up around 166vdc
( uses the peak vac which is around 170vac.)
For a 150vdc max controller ( midnite 150) or a 144vdc ( outback FM) then a
buck transformer or standard transformer is the trick to reduce the AC and
hence the DC for these lower voltage units.
jay
peltz power
On Dec 15, 2014, at 5:38 PM, Kirk Herander wrote:
This has been discussed on this list in years past. It is possible to use an
outback charge controller as a battery charger. You need to put the 120 AC
into a bridge rectifier, then feed the 120 DC into the controller's PV
input. So you'll have an 80 amp battery charger.
Kirk Herander
VT Solar, LLC
Proven PV provider since 1991
www.vermontsolarnow.com <x-msg://519/www.vermontsolarnow.com>
dba Vermont Solar Engineering
NABCEPTM Inaugural Certificant
VT RE Incentive Program Partner
802.863.1202
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Dan Tittmann
Sent: Monday, December 15, 2014 8:18 PM
To: info at windsine.org; RE-wrenches
Subject: Re: [RE-wrenches] Programmable Battery Charger
You can manually adjust Iotas with tweaking the potentiomiters while
monitoring it with a god volt meter. But no time adjustment.
Daniel
Daniel Tittmann
CTO
Greenwired
www.greenwired.com
daniel at greenwired.com
707-923-2001 (office)
707-206-5088 (Cell)
On Mon, Dec 15, 2014 at 4:21 PM, Windsine Inc. <windsine at gmail.com> wrote:
Check out Argus Technologies.
RoyR
On Dec 15, 2014 4:01 PM, "Larry" <larry at starlightsolar.com> wrote:
Wrenches,
Does anyone know of a 120/12 volt battery charger that can be programmed for
absorb and float voltage and time in absorb mode? I have been needing this
product for many years but I can only find it in inverters with built in
chargers from Magnum, Outback, and Xantrex.
--
Thank you,
Larry Crutcher
Starlight Solar Power Systems
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141216/b9b7aa5a/attachment.htm>
More information about the RE-Wrenches
mailing list