Hi Mac,
Jay just had the same issue and it was 120v from the gen instead of 120/240. The inverter was charging using half the windings causing it to Overtemp.
Check the 60A breakers on the side of the inverter. Also make sure to remove the wires from the input terminal block before measuring voltage as the inverter will make 120v look like 120/240v at the terminals.
If the generator is 3 Phase it won't work with this inverter unless you only use one leg. This will work but you will need to turn the charge rate to 50% in order to prevent Overtemp. Sometimes it works as high as 70%.
Gary Baxter
Product Manager
Magnum/Dimensions
On Dec 15, 2014, at 12:12 PM, Mac Lewis <maclewis1 at gmail.com<mailto:maclewis1 at gmail.com>> wrote:
Hi jarmo,
We have verified this is split phase 120/240. My multimeter gets 120 L-N and 240 L-L.
Thanks
On Dec 15, 2014 10:25 AM, <Jarmo.Venalainen at schneider-electric.com<mailto:Jarmo.Venalainen at schneider-electric.com>> wrote:
Hi:
The Generac QT02224GNAX ships as a three-phase 120/208 VAC. I believe the Magnum is a 120/240 VAC.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA | Training & Development Specialist - Senior
Phone: +604-422-2528<tel:%2B604-422-2528> | Fax: +604-420-1591<tel:%2B604-420-1591> | Mobile: +604-505-0291<tel:%2B604-505-0291>
Email: jarmo.venalainen at schneider-electric.com<mailto:jarmo.venalainen at schneider-electric.com> | Site: www.SEsolar.com<http://www.sesolar.com/> | Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
<mime-attachment.jpg><http://%20www.sesolar.com/>
*** Please consider the environment before printing this e-mail
From: Mac Lewis <maclewis1 at gmail.com<mailto:maclewis1 at gmail.com>>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>,
Date: 12/15/2014 05:52 AM
Subject: [RE-wrenches] Generac QT series
Sent by: "RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>>
________________________________
Hello wrenches,
We have a newly installed system that has a 22 kW Generac Quiet Source QT02224GNAX with a Magnum MS4448-PAE. When we start the generator, the Magnum's internal transformer temperature climbs to overtemp (240F) within a 2 minutes. The batteries are being floated at the time, and haven't seen more than 5A coming out of the generator. We swapped the Magnum out, and we have the exact same issue. We then got a job-site gas generator 6500W and ran it. No problem whatsoever. The problem appears to be with the Generac, or with the interaction between the Generac & the Magnum. I didn't have a scope on site but the fluke multimeter doesn't detect anything wrong with the voltage or frequency coming from the Generac.
Has anyone had issues with the Generac QT? Anyone paired one with a Magnum PAE before? I want to get my scope up there and look for triplen harmonics, but I'm not sure how to filter these out. Any references on how to effectively do that is appreciated.
Thanks in advance
--
Mac Lewis
"Yo solo s? que no s? nada." -S?crates
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
_____________________________________________________________________________________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141216/ad6b96c5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ATT00001.jpg
Type: image/jpeg
Size: 14092 bytes
Desc: ATT00001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141216/ad6b96c5/attachment.jpg>
More information about the RE-Wrenches
mailing list