Hi:
I've never been on a site where I've seen this either. That's one reason
why I find this group so interesting.
For me it makes sense if you consider the following,
1. The only difference between the positive and negative plate in a
flooded lead-acid battery is the lead compound that was pressed and cured
onto it during manufacture. When fully charged, the negative plate is
mostly Lead and the other mostly Lead Oxide.
2. The charge-discharge equation is:
3. If you fully discharge, (I mean to the bitter end), then all of the
Lead, Lead Oxide and acid has been turned into Lead Sulphate and pretty
much pure water.
4. If you can get some current to flow through the pure water, (sulphation
crystals and the poorly conducting pure water in between the plates is one
reason why dead batteries initially "wont accept a charge"), then when it
starts charging, I guess the battery doesn't care which plate it starts
depositing the Lead and Lead Oxide onto.
5. With a string of 24pcs of 2 volt cells, if 16 of them are making the
proper voltage and 8 of them are 100% dead with no voltage, then the
voltage applied by the good cells will appear as a reversed voltage on all
the dead cells.
6. The dead cells see this as a charging voltage which causes the Lead and
Lead oxide to begin forming on the wrong plates.
7. As long as there is persistent load on the bank which refuses to go
away at any voltage, then I suppose in the limit, the reversal could
happen in up to 1/2 of the cells in the battery bank.
For your site, it means regardless of what else may have happened, there
must have been a persistent load on the batteries with no active charging
source present.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA |
Training & Development Specialist - Senior
Phone: +604-422-2528 | Fax: +604-420-1591 | Mobile: +604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.SEsolar.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From:
Jay Peltz <jay at asis.com>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>,
Date:
12/19/2014 11:54 AM
Subject:
Re: [RE-wrenches] Magnum System - Discharged Battery Bank
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
I find it really curious.
I've been dealing with batteries for almost 20 yrs. I've seen so many
dead, flat batteries, systems etc I can't count them all.
But I've yet to find a reversed one.
I understand the process.
I'm trying to understand how he could get multiple reversed batteries at
one go?
Jay
Peltz power
Sent from my iPhone
On Dec 19, 2014, at 9:47 AM, Jarmo.Venalainen at schneider-electric.com
wrote:
Hi:
This cell reversal ability of lead acid batteries gives good perspective
on just how much you can mistreat them and beat them up and still have an
expectation of "recovery".
Lithium cells on the other hand without a full range of protections would
have long since filled the home with all kinds of interesting high
temperature thermal events, gaseous compounds and chemicals, and there is
no way you could get that magic smoke back into them.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA |
Training & Development Specialist - Senior
Phone: +604-422-2528 | Fax: +604-420-1591 | Mobile: +604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.SEsolar.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
<mime-attachment.jpg>
*** Please consider the environment before printing this e-mail
From:
Corey Shalanski <cshalanski at joule-energy.com>
To:
re-wrenches at lists.re-wrenches.org,
Date:
12/19/2014 06:48 AM
Subject:
Re: [RE-wrenches] Magnum System - Discharged Battery Bank
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
Update on my investigation:
I visited the customer's house yesterday to set up a pulse charger. Much
to my surprise the three batteries that originally registered negative
voltage are now reading positive. Does this make sense - are batteries
able to shift between negative and positive voltages at such a low charge
level?
I do not see any evidence of distorted cases.
On Thu, Dec 18, 2014 at 7:58 AM, <jay at asis.com> wrote:
I second tump.
Most likely a bad /cell battery took out the system.
As these are VRLA batteries, I'm curious do,the cases look damaged such as
expanded or sunk in?
Jay
Peltz power
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141219/9f46889e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 142681 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141219/9f46889e/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14812 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141219/9f46889e/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14092 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141219/9f46889e/attachment.jpe>
More information about the RE-Wrenches
mailing list